JohnMo Posted June 8 Posted June 8 20 minutes ago, Mr Blobby said: We have approx 200 litres, so I take it the manual is correct and an extra expansion vessel is required? That sounds a lot, are you sure? But if correct, you will need an additional expansion vessel. Too much expansion room is better than not enough.
Mr Blobby Posted June 8 Author Posted June 8 13 minutes ago, JohnMo said: That sounds a lot, are you sure? Ha, you're right, I used 16mm diameter for the UFH pipes, but the internal diameter is of course less. 😆 At 12mm ID the volume is just 118. That's more like it 🙄
SimonD Posted June 8 Posted June 8 28 minutes ago, Mr Blobby said: The plumber (and hence the builder) are adamant that I need to mount it on rubber feet, despite advice from Panasonic to bolt the unit to the slab. We'll see. You don't need rubber feet on the Panasonics and you don't need to go to the expense of flexi connections to the heat pump either. You can buy and fit rubber feet if you want to and there is also a mounting frame available (with adjustable feet for uneven ground) if you need to install at greater height but this is usually only used for snow clearance. Yep, add another expansion vessel - shame it's not like the Viessmann boilers where there's a specified test procedure you can follow to determine if the built in vessel is sufficient, but it's quick and easy to add another.. 36 minutes ago, Mr Blobby said: A commissioning service is offered but no detail on pricing etc so I'm going to try to get this up and running myself. Given your UFH installation, a full commissioning service to balance your UFH will likely take days to do properly given the lag in a slab and also is best done when it's cold out. Just buy yourself a few pipe thermostats and stock up on patience. On 27/05/2026 at 13:05, JohnMo said: We have relaxed (simplified )that control and just use a room sensor to control everything, Wow, I'm glad I was sitting down when I read this. @JohnMo has joined the dark side and gone room influence. I never thought I'd ever see the day given how adamant you used to be that it was akin to the devil 😉 What changed? Or is this another experiment? 1
Mr Blobby Posted June 8 Author Posted June 8 (edited) We have a concrete pad already poured for the unit to sit on. Its a few inches above ground level. Just seen this in my whatsapp from plumber/builder 🤷♂️ Edited June 8 by Mr Blobby
JohnMo Posted June 8 Posted June 8 38 minutes ago, SimonD said: Wow, I'm glad I was sitting down when I read this. @JohnMo has joined the dark side and gone room influence. I never thought I'd ever see the day given how adamant you used to be that it was akin to the devil 😉 What changed? Or is this another experiment No not room influence - whole house, one room sensor/thermostat for whole house. Hiaer doesn't have a thermostat built into the controller. It is connected to outside temperature sensor so also allows oat switching the whole heat pump off in heating mode when outside is an average (over 6 hrs) above 10 degs. No need to get excited, still single single zone, WC, no actuators, just an on off permission, mostly because running heat pump at 9 degs OAT on full WC at about 22 degs doesn't work, which is about the temperature it needs at that temperature. So heat pump uses a simple permission to run at 26 degs, runs for a couple of hours and then shuts off for about 18 hrs. The colder it gets the longer the run time. No setbacks just single room temperature 24/7. But really needed for cooling as I run a set flow temp with humidity over ride. So makes sense to flick a single switch that takes thermostat from heat cool and same switch moves ASHP between heat cool also.
JohnMo Posted June 8 Posted June 8 32 minutes ago, Mr Blobby said: Just seen this in my whatsapp from plumber/builder I used these to get the snow clearance needed to comply with OEM requirements for snow. https://www.wolseley.co.uk/product/pump-house-1000mm-condensing-unit-mounting-block/?pid=P667987
SimonD Posted June 8 Posted June 8 24 minutes ago, JohnMo said: No not room influence - whole house, one room sensor/thermostat for whole house. Hiaer doesn't have a thermostat built into the controller. It is connected to outside temperature sensor so also allows oat switching the whole heat pump off in heating mode when outside is an average (over 6 hrs) above 10 degs. No need to get excited, still single single zone, WC, no actuators, just an on off permission, mostly because running heat pump at 9 degs OAT on full WC at about 22 degs doesn't work, which is about the temperature it needs at that temperature. So heat pump uses a simple permission to run at 26 degs, runs for a couple of hours and then shuts off for about 18 hrs. The colder it gets the longer the run time. No setbacks just single room temperature 24/7. But really needed for cooling as I run a set flow temp with humidity over ride. So makes sense to flick a single switch that takes thermostat from heat cool and same switch moves ASHP between heat cool also. Hehe, what you've described is room influence, although the best room influence simply sends an additional signal to the heat pump to reduce the flow temps essentially modifying the WC curve. But if you have control from the room, that's room influence as it calls to the heat pump - nothing to do with actuators/open loop in an of themselves. Room influence is just about adding additional system control which uses the room conditions as input. 😁
SimonD Posted June 9 Posted June 9 20 hours ago, Mr Blobby said: We have a concrete pad already poured for the unit to sit on. Its a few inches above ground level. What exact Panasonic model are you installing?
Mr Blobby Posted June 9 Author Posted June 9 5 hours ago, SimonD said: What exact Panasonic model are you installing? J Series mono-bloc. 5kW. https://www.aircon.panasonic.eu/GB_en/product/aquarea-high-performance-mono-bloc-j-generation-r32/
SimonD Posted June 9 Posted June 9 9 minutes ago, Mr Blobby said: J Series mono-bloc. 5kW. https://www.aircon.panasonic.eu/GB_en/product/aquarea-high-performance-mono-bloc-j-generation-r32/ Ah, okay. How come you chose that over the newer r290 L series? Any particular technical reasons other than that the L series has to have an indoor unit?
Mr Blobby Posted June 9 Author Posted June 9 So the heat pump has been delivered and it looks like it may actually be anthracite, which is remarkable, though it is difficult to see without taking all the cardboard off. The heat pump manual states 22mm flaw and return. I told the supplier this and I told him I did not want to "upgrade to 28mm". The plumber subsequently spoke to his contact at the suppliers and the heat pump has turned up with 28mm bends (that were no on the original invoice I saw) and 28mm AF valves, and 28mm stop valves. The flow rate for this heat pump is just 14 l/min. I imagine that is why the external pipework is specified at 22mm to maintain the velocity and minimise potential heat loss. I texted the plumber yesterday to tell him that the pipework had to be 22mm, I guess I was too late and the supplier and plumber agreed to use 28mm regardless my instruction or panasonic specification. The holes cored in the wall are sized for 22mm pipe and insulation, which I have on site. I suppose that, with the 28mm bends and stop valves and AF valves that have been delivered, the plumber intends to install these and then reduce to 22mm. It may be that the holes cored in the wall, or at least one of them, is too low, so that the AF valve may need to be installed at the lowest point being the entry into the house, and not at the HP end, hence the 28mm valve may sit in the middle of 2 lengths of 22 mm copper. Should I put my foot down and insist on 22mm AF valves and ball valves, or is it not a big deal?
Mr Blobby Posted June 9 Author Posted June 9 (edited) 8 minutes ago, SimonD said: Ah, okay. How come you chose that over the newer r290 L series? Any particular technical reasons other than that the L series has to have an indoor unit? You guessed right, I didn't really want a split unit. And also they are marketed as high temperature units, where I don't expect to ever want to go above 45 or 50 degrees for HW, much less for heating. .. and they cost about a grand more. Edited June 9 by Mr Blobby
SimonD Posted June 9 Posted June 9 14 minutes ago, Mr Blobby said: Should I put my foot down and insist on 22mm AF valves and ball valves, or is it not a big deal? I think you need to have a word with them. As you say, with 5kW which won't be running at that for much of the time (other than during dhw), the 28mm pipe is just too big. Tell them to sort themselves out and do it properly. There is the option to use compression reducers with those fittings and use 22mm pipe for the rest of it - there are some pieces of equipment that only come with 28mm compression but the manufacturers chuck in the reducers for 22mm situations in the box. But what do you mean by 28mm bends - not flexis surely as these units don't need flexis. 1
Mr Blobby Posted June 9 Author Posted June 9 (edited) Thank you @SimonD for your response, which pretty much confirms my sentiment that they need to do it right, rather than what they always do. What pees me off is the way these 28mm components turn up without any discussion when I have already asked for 22mm connections, as per the Panasonic install guide. So the 1 1/4 28 mm AF valves are ok enough to use with reducers? I'm not sure what end of the pipe the valves sit and going 22 pipe ---> 28 AF valve ---> 22 pipe seems daft. 1 hour ago, SimonD said: But what do you mean by 28mm bends - not flexis surely as these units don't need flexis. Sorry, excuse the layperson language, I mean elbow. Two 28mm press fit elbows were added to the order, they look like this https://www.screwfix.com/p/flomasta-copper-press-fit-equal-90-m-profile-elbows-28mm-2-pack/591ak Edited June 9 by Mr Blobby
Mr Blobby Posted June 9 Author Posted June 9 AF valves are 1 1/4. I think the plumber and supplier have assumed the AF valves connect directly to the 1 1/4 inch connecter on the side of the heatpump. Which may not be the case.
SimonD Posted June 9 Posted June 9 4 hours ago, Mr Blobby said: AF valves are 1 1/4. I think the plumber and supplier have assumed the AF valves connect directly to the 1 1/4 inch connecter on the side of the heatpump. Which may not be the case. No, you don't really want these connected directly to the unit - ideally just at the lowest part of the system to ensure drainage if ever needed. Normally there will be a length of pipe off the heat pump, AF valves and then the full bore lever valves. The AF valves should also not be installed one on top of each other unless they come with the guard. I always order the Inta zero AF valves with the guards as I've always been able to get them cheaper than the valves without the guards, believe it or not. E.g. https://www.bes.co.uk/inta-zero-anti-freeze-valve-28mm-compression-25790/ https://www.bes.co.uk/inta-zero-anti-freeze-valve-28mm-compression-offer-28132/ You can obviously make your 1 1/4 ones work - I'm guessing they're swivel on one side? Are they then 28mm compression on the other or just BSP on both sides? With the 28mm compression, just use these https://www.bes.co.uk/pipe-tube-fittings/pipe-fittings/compression/reducing-set-28-x-22mm-compression-17740/ as Inta Zero, probably the most popular one out there, only come in 28mm as minimum, but Caleffi supply 22mm compression AF valves. Given what you've said I'm actually quite worried about who you've got coming to do the job.... who is actually doing the commissioning and registering the warranty? And have you planned to install the remote control to get the extended 7 years?
Mr Blobby Posted June 9 Author Posted June 9 (edited) So the AF valves delivered are Caleffi 108. Model 108701. https://www.advancedwater.co.uk/product/caleffi-antifreeze-valve-1-14-108701 1 hour ago, SimonD said: You can obviously make your 1 1/4 ones work - I'm guessing they're swivel on one side? AFAICS, no swivel on one side. On the quote the ball valves were like this... https://www.intatec.co.uk/products/k-type-extended-ball-valve/ But what has been delivered is this cheaper substitute, which isn't good: The 3 way valve is this VC6013MP6000 1 inch. Like this. https://www.kestakon.co.uk/3-way-valve-1-it-vc6013mp6000-honeywell-without-limit-switch/ Added to the delivery were 6 x 28 mm to 1.1/4 compression straight fittings and the two 28mm elbows. So I think I'll swap out the components for 22mm AF valves if I can get them, and decent, not economy, 22mm ball valves. Then it should be possible to connect the pipework from heatpump into the house without so many reducers everywhere. I think. 🤔 Perhaps the lesson here is to specify everything instead of relying on the heat pump supplier to configure the plumbing components. 1 hour ago, SimonD said: Given what you've said I'm actually quite worried about who you've got coming to do the job.... who is actually doing the commissioning and registering the warranty? The people who supplied the heat pump do offer to do commissioning and sign off for the warranty but as yet have given no price for this service. I'm in no rush to ask them to do so. The first supplier we approached didn't even give us a price because I refused to have a buffer tank. I reckon our plumber can do all the wet work, our electrician the wiring. It may be that the risk of heat pump failure is too small and the cost of commissioning too high to make the the extra warranty worth it. I'll soon find out 😬 Edited June 9 by Mr Blobby
SimonD Posted June 10 Posted June 10 10 hours ago, Mr Blobby said: I reckon our plumber can do all the wet work I'm actually quite worried about your plumber if he/she has been involved in spec. and supply of the components. Definitely insist on what you've ordered. The extended ball valves are a blessing as you want the valves fully insulated and accessible. It's possible to do it with the normal valves but not as neat - I don't know whether the cheapo ones you've receive are even full bore? Using bsp to compression fittings is not too much of a problem, but to me it's the unnecessary cost because the bsp valves plus fittings are always more expensive than just buying the compression ones and then you have the additional joints - and there's the additional time fitting them which can be quite significant. It may be a good idea to just sit down and draw your pipework section from heat pump to wherever the primary flow/returns are going and then map out exactly what fittings are going where and then sit down with the plumber and give the supplier a kick with the resulting list and exchanges. Good luck.
Mr Blobby Posted June 10 Author Posted June 10 Thanks. It's all oil heating here in Northern Ireland so heat pumps are a bit of a challenge. Once we get inside the house then the plumbing should be the same as any other system so I'm trusting my plumber to do all that wet stuff with his eyes closed. One last question, do you have a link to an extended ball valve 22mm, I think they are all 28. Or maybe I run 28 mm to the end of the ball valves and then reduce down to 22 🤔
JohnMo Posted June 10 Posted June 10 58 minutes ago, Mr Blobby said: ball valves and then reduce down to 22 Generally all heat pump stuff is 28mm and bigger. If your pipe runs are short 22mm is fine, if they are long 28mm may be better. Valve https://www.unventedcomponentseurope.com/inta-1-female-swivel-x-1-male-heat-pump-extended-lever-ball-valve-hpbv11.html/?utm_source=Google Shopping&utm_campaign=Copy Unvented Components Europe&utm_medium=cpc&utm_term=adtribes&gad_source=1&gad_campaignid=17178278874&gbraid=0AAAAADCTOYDIF7_WqM1JdaR45hjcYe7rN&gclid=Cj0KCQjwlqTRBhCBARIsANrkrxiP5YU1oqx-01ITZliqfzcXOrTDlwcJv1dfpMhdWYFUDscVx6Kw2D0aAtV4EALw_wcB
SimonD Posted June 10 Posted June 10 1 hour ago, Mr Blobby said: One last question, do you have a link to an extended ball valve 22mm, I think they are all 28. Or maybe I run 28 mm to the end of the ball valves and then reduce down to 22 🤔 Intatec do them: https://www.intatec.co.uk/products/k-type-extended-ball-valve-2/ but this is probably special order from your local friendly merchants. However, the standard ball valve just about work with external pipe insulation - I've used them quite a lot.
Mr Blobby Posted July 13 Author Posted July 13 The heat pump is installed 😀. And its anthracite. And thanks to guidance on here, the single zone, two manifold system is running beautifully. No buffer, no pumps, no mixers, its as simple as can be. These Panasonic units seem incredibly easy to install and set up. I'm struggling to see why it needs to be commissioned by a Panasonic Pro partner. I'm not sure how they are going to add any value. Except for the extended warranty. 1
Recommended Posts