EinTopaz Posted Monday at 16:43 Posted Monday at 16:43 (edited) Hi all, Was recently looking at replacing the soffits and facias over a front bay window, on closer inspection It looked like there was potentially a void in the outer skin of the wall that the soffits, facias and the roof of the bay window are covering. I decided to take some tiles off to have a better look and did indeed find a void in the outer skin of the wall, and to my eyes looks like the void continues through the inner skin too? (though it'd be good for someone to confirm that). Based on the image and video below, how bad of a problem is this? should I get the roof off and seal this void? Reason I ask is because this bay window is for the dining room, notably the coldest room in the house. So perhaps not a coincidence? Here's a video that shows the void well :- Hole Video Behind Bay And images too:- Bay window in question Void behind the tiled roof. What do you guys think? fine? or bad? or really bad? thanks Ged Edited Monday at 16:47 by EinTopaz
Nickfromwales Posted Tuesday at 12:39 Posted Tuesday at 12:39 The internal leaf of masonry should be a continuous ‘layer’, so draughts can only travel through the cavity. What we’re seeing is typical ‘builder quality’ work for that era. 1
Tony L Posted Tuesday at 16:38 Posted Tuesday at 16:38 3 hours ago, Nickfromwales said: ...typical ‘builder quality’ work for that era & the current era as well, if the builders & architectural technicians I have employed are representative of today's building industry personnel. 1
EinTopaz Posted 2 hours ago Author Posted 2 hours ago thanks guys. It looks to my eye that neither of the leafs are continuous based on that.... and looks like they'd foamed the outer once but either not all the way across or its failed. For a fix, tiles, battens, felt off.... PIR board wedged in as deep as I can get it, and foam sealed around the edge, will that suffice? For trivia....Worth noting the property used to be a bungalow so those bays will have originally just run into the old roof. It was converted in 2006 so had hoped i wouldn't be finding this but hey ho, it is it what it is. picture of it in its original bungalow form...
Mr Punter Posted 2 hours ago Posted 2 hours ago If it was done in 2006 there may be some drawings. You would think there would be a beam or lintel spanning above the window to support the masonry for the new first floor.
EinTopaz Posted 23 minutes ago Author Posted 23 minutes ago There likely is, but i think it may be even higher up than this, Every bedroom on the 1st floor of this property steps up 100mm towards the front of the house, so I reckon the lintel is in there. All the voids between floor and ceiling have double cavity voids too. Where I think they kept the original bungalow ceiling up, then essentially did another cavity above that. Its an odd one. But either way; is the fix to basically PIR board that huge gap and foam seal?