Hello All!

 

We have a ground floor extension underway, and I need to get the drainage from the existing upstairs bathroom sorted before the roof can go on.

We're adding a new W/C downstairs which has necessitated moving the soil stack over a few meters. (The underground drainage is already in place and signed off by building control with the upstairs W/C connected temporarily.)

Moving the soil stack leaves me with the problem that the bath waste is now more than 4m away. I understand the max run for 40mm waste is up to 3m, and 50mm is up to 4m.

This is what I have in mind.

Blue = 40mm bath waste
Green = 32mm basin waste
Red = 110mm

I was thinking it would be sensible to put rodding points in at A & B (with inspection covers internally).

I'm planning to use one of these (or similar) for the 40mm to 110mm connection.

 
image_2026-01-18_164338389.thumb.png.b7d78190c246f00c6d060cec19b21c88.png
 
 
 
1768752120642.png


Here's the house / extension in profile, so you can see that most of this pipework will be boxed in internally.

 
1768752350903.png


So you can see the full picture, this is the arrangement of the upstairs W/C, showing what it would look like if 40mm pipe was used for the full run.
 
1768752477665.png





The last diagram also shows the boiler condensate which I need to re-route into the bath waste. I plan to get this particular bit done by a Gas Safe registered plumber, but I'd still like to have a vague understanding of what needs to happen here so I can plan the other pipework accordingly - I'm not sure it's quite as simple as plumbing the condensate drain into a tee below the bath.

Does the arrangement look OK (ie., compliant with building regs), and does anyone have any clues on what needs to happen to plumb the condensate drain into the bath waste?

Thank you for any advice!
 
 
 

I may have misunderstood, but if 40mm is limited to 3m, how is your 4.5m run (with a 90 deg bend in) OK? And is the length limitation about potential siphoning, or about the need for a rodding eye? If the latter then I can see how you could 'engineer' a rodding eye at the 90 deg bend so that it truly is 3.1m and 1.4m, but if it's about potential siphoning then you still have at least a theoretical problem...? Can you clarify?

  • Author
10 minutes ago, Redbeard said:

I may have misunderstood, but if 40mm is limited to 3m, how is your 4.5m run (with a 90 deg bend in) OK? And is the length limitation about potential siphoning, or about the need for a rodding eye? If the latter then I can see how you could 'engineer' a rodding eye at the 90 deg bend so that it truly is 3.1m and 1.4m, but if it's about potential siphoning then you still have at least a theoretical problem...? Can you clarify?

 

Sorry, I've just realised that isn't too clear.  

 

This is what it would look like from inside the bathroom, so under 3m of 40mm from the bath. I'm just unsure about the transition into the 110mm, as I haven't seen it done this way before...

 

image.thumb.png.facf06f03d0ff5d01a3ddb78c5c71573.png

I suspect you'll get horrible gurgling in the bath and sink if there's no air admittance valve upstream of the basin.  Otherwise generally "better" to drop into the main sewer from the top rather than end (cap the end for rodding) - but you may not have enough fall available for that at the moment, and what you have in mind will work.

  • Author
14 minutes ago, MPx said:

I suspect you'll get horrible gurgling in the bath and sink if there's no air admittance valve upstream of the basin.  Otherwise generally "better" to drop into the main sewer from the top rather than end (cap the end for rodding) - but you may not have enough fall available for that at the moment, and what you have in mind will work.

 

Would one of these fitted to the basin help?  Or do you think I would still have the same problem with the bath?  

 

McAlpine 32mm Anti-Syphon Bottle Trap - A10V Large Image

  • Author

Or I could try to get an AAV in here (in orange)...but it would be tough to get it above the basin trap height.

 

image.thumb.png.9a2bdd49df5af214b0f1ceb2885a424c.png

The pipe off the 110mm should be 50mm up to where it heads in to the bath, turning in on a T with a rodding access (cleaning eye) for maintenance.

 

From the 50mm T you reduce to 40mm to get to the bath T, and then the 40mm pipe continues to the boiler. 
 

That then terminates at a 40mm T with the centre of the T having a 40 > 21.5mm reducer in it for the boiler condensate, and a 40mm air admittance valve to complete the run.

 

Absolutely ZERO need for a GSR plumber, this will just add wasted expense.

  • Author
2 hours ago, Nickfromwales said:

The pipe off the 110mm should be 50mm up to where it heads in to the bath, turning in on a T with a rodding access (cleaning eye) for maintenance.

 

From the 50mm T you reduce to 40mm to get to the bath T, and then the 40mm pipe continues to the boiler. 
 

That then terminates at a 40mm T with the centre of the T having a 40 > 21.5mm reducer in it for the boiler condensate, and a 40mm air admittance valve to complete the run.

 

Absolutely ZERO need for a GSR plumber, this will just add wasted expense.

 

Thank you Nick!

 

Just to confirm - is this roughly correct?

 

Red = 110mm

Grey = 50mm

Green = 32mm

Blue = 40mm

Yellow = 21.5mm

 

image.png.de088d0a3eaefa3d32a498b2a2fc7a2c.png

 

 

On the other side of the wall, is this what you mean?

 

image.thumb.png.13d0bdc8bd0224d4bc12362759e202ad.png

One of the reasons I was going to get a plumber in for this was the mention of a trap in Approved Document H...is this necessary?

 

 

image.png.6ad457fe1c8998401b6e71041fba1dd8.png

image.png.2a102d48cf66cebb87d50d3a1f7a1161.png

 

 

  • Author
10 hours ago, Nickfromwales said:

Boilers usually have the trap inbuilt ;). I’ve fitted more gas boilers than I care to remember, and we’ve never had to fit a 3rd party trap. 
 

And yes, your pic is spot on. 

 

Thanks again!   Have confirmed the Gloworm boiler we have is fitted with an inbuilt trap 👍

 

Is this the best way to orient the blanking cap for rodding?  Looking at it I feel like I should turn it through 90° so debris doesn't collect...

 

image.png.df22d3ee7fbe0a624b81448b9c300566.png

 

 

And...hopefully last question - can the AAV go at any height as long as it's more than 200mm above the highest water inlet?

27 minutes ago, Allthegearnoidea said:

 

Thanks again!   Have confirmed the Gloworm boiler we have is fitted with an inbuilt trap 👍

 

Is this the best way to orient the blanking cap for rodding?  Looking at it I feel like I should turn it through 90° so debris doesn't collect...

 

image.png.df22d3ee7fbe0a624b81448b9c300566.png

 

 

And...hopefully last question - can the AAV go at any height as long as it's more than 200mm above the highest water inlet?

You can turn the T and still get a thin rod up to the bath, so no worries there.

 

Water will come out of the WC pan before it gets anywhere near that high, but rule of thumb is as you show. 200mm is plenty, but you can go higher, just no point afaic. 

  • Author
24 minutes ago, Nickfromwales said:

You can turn the T and still get a thin rod up to the bath, so no worries there.

 

Water will come out of the WC pan before it gets anywhere near that high, but rule of thumb is as you show. 200mm is plenty, but you can go higher, just no point afaic. 

 

Great, I have a plan now - thanks again 👍

  • 3 weeks later...
  • Author

Right, I've made it to the outside and need to figure out the arrangement here...

 

Hopefully it's clear that the original / temporary stack is to be removed and the new stack is going over to the right. 

 

Option A - I personally prefer this because it gives me a sharp drop immediately after the WC outlet - similar to the way it was installed originally which has always worked very well.

 

image.png.5ccf0d7f50dc0e5c04650342de6951f8.png

 

Its a bit lower, but still around 2.4m at the join to the new stack

 

Option B - seems more conventional, about 200mm higher.  Might end up having to use a strap boss for the 50mm pipe at the stack which I don't really like. 

 

image.png.385f47a920612a9ce3d329a765cd963d.png

 

What's the preferred way to do this, and whereabouts are inspection / access covers recommended?  

 

Pipework all to be boxed internally:

 

image.thumb.png.f1ac9c0ee2814f1af8b470dcedba541f.png

 

Edited by Allthegearnoidea

  • Author

Option C - Previously the basin and bath went into a hopper where you can see the two temporary downpipes, these are currently just feeding into the old drain which is still there below the slab and working - ie., A & B join up underground anyway.  Reading the regs again, it does say that boiler condensate should be downstream of a sink (basin?), so maybe it's best to use this and box it in after all?  It would still be vented at the boiler end.

 

image.png.3f4c69a35f990b9b39baa9cc4b49df6f.png

 

image.png.3ef617540e670b99f9e5805790c81ffb.png

 

Edited by Allthegearnoidea

  • Author
5 hours ago, Nickfromwales said:

What about opening the window? 

 

Sorry, I should have made that clear.  We haven't broken through yet, but there will be a new internal opening, roughly as below - window will be bricked up when we get to that stage.

 

image.png.e949ffa73912226ffbb16e27beac34a8.png

 

I could box the suggested pipework into that corner (A), but ideally I'd still run 50mm down the wall as far as possible to keep it tight.

 

image.png.90cb490cd649b52f40d0c98f68b178a7.png

 

 

I've learned this is known as a stub-stack?  They're only supposed to serve one storey if I'm understanding the regs correctly - which it would, being the upstairs bathroom (the white tee you can see going through the wall goes to the washing machine in the garage, but I could divert that off elsewhere to make building control happy).

 

This way the condensate waste is downstream of the basin so I don't need to run two pipes, and it isn't too cramped or long. 

 

Not sure which way to go - this one seems the most straightforward for my plumbing skills, but feels like building control might raise an eyebrow?  Option A, someone commented if the toilet blocked it could back up to the basin?

 

Raining on it all day today anyway, luckily I'm not too worried about a bit of water getting into the cavity where I've knocked through behind the loo since I'm knocking that wall out anyway, but I've covered it over anyway to make myself feel better 😁   

 

 

 

 

 

Edited by Allthegearnoidea

  • Author

Final answer 🤣

 

32 > 40mm for the basin as it is more than 1.7m

Boiler / bath waste 40 > 50mm and downstream of the basin

Inspection bend at rear of WC

 

image.png.f9cab011f18e66f667e2e02104449e65.png

 

My 'stub stack' idea is no good, branch would be too high above invert of stack.

 

Edited by Allthegearnoidea

17 hours ago, Allthegearnoidea said:

Final answer 🤣

 

32 > 40mm for the basin as it is more than 1.7m

Boiler / bath waste 40 > 50mm and downstream of the basin

Inspection bend at rear of WC

 

image.png.f9cab011f18e66f667e2e02104449e65.png

 

My 'stub stack' idea is no good, branch would be too high above invert of stack.

 

Where the new 110mm pipe travels horizontally to meet the new stack, just lower that so you can come out of the house, and drop down into a branch, and then the 50mm waste goes into the back of the branch. Saves the long 50mm waste run to the stack.

  • Author
5 hours ago, Nickfromwales said:

@Allthegearnoidea

 

Worlds shittest drawing, free-styling off my iPhone atm, but should explain what I mean. 
 

image.thumb.jpeg.f4da32fc27f8923e1d10a50d2860a4a8.jpeg

 

Perfectly clear, thanks Nick 👍

 

38 minutes ago, Allthegearnoidea said:

 

Perfectly clear, thanks Nick 👍

 

Use a Y-branch (135 degree) and not a T ;) Put a 'single socket' 135 bend in the branch, and then go vertical to pick up the WC. That means when the goods in transit hit the branch they're already heading towards the stack, instead of dropping into a T with a "thud".

 

https://skyplastics.co.uk/pushfit-135-deg-triple-socket-branch-110mm-black.html?gad_source=1&gad_campaignid=11823408165&gbraid=0AAAAACepU-bFP3X5wMqLbWz1M4ZiHqX2W&gclid=Cj0KCQiAy6vMBhDCARIsAK8rOgldyshF_iNQbKD8AmrMjpPTNH97RAhWJvgKNEN-Zg3keFU2keaNwhUaAp4XEALw_wcB

 

https://skyplastics.co.uk/110mm-single-socket-135-bend-2.html

 

One of these in the open end of the branch, with the 50mm inlet at the bottom. Use a couple of 135 degree spigot (45's) in 50mm to jump into that.

 

https://skyplastics.co.uk/110mm-reducer-to-50mm-waste-pipe.html

 

I think this goes into the adaptor, but ring and check if you buy from here (good prices!).

 

https://skyplastics.co.uk/50x-63mm-solvent-boss-adaptor-black-olivw-grey.html

 

Then push the 50mm pipe in and job done.

 

They've got black 50mm pipe and fittings / clips etc.

 

https://skyplastics.co.uk/50mm-x-3-metre-solvent-weld-waste-pipe.html

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.