November 27, 2025Nov 27 Hi everybody. Our 2002 Baxi 105e instant has been (and still is) a cracking good boiler, but of late it is becoming increasingly unreliable with niggly random issues mainly around control items. I've done numerous jobs on the water set over the years, including swapping out the PCB, thermistors, and other bits which are still readily available just about anywhere. The latest iteration of what can be described as 'random' faulting, is that the boiler locks out when you shower whilst the system is calling for heat; you are then left with the flashing 50C LED and DHW symbol, and the pump running continuously. Powering off for half an hour and reconnecting sees the boiler run its usual ignition check and hey presto, all back to normal! Central heating functions as normal, and DHW as well, just not both together. I'm guessing the overheating is something to do with the diverter valve (the DHW diaphram is new) but my wife has pointed out that the boiler is probably at the end of its service life, is less efficient and more polluting than a replacement, and she would be stuck if I wasn't around when these things happen. All this is very true, so I'm looking for a replacement. The Baxi Duo Tec 28 is the replacement I'd go for, as it sits on the same jig and has the same pipework/flue configuration. I'm not looking for big efficiency savings here, just another boiler that will last 15-20 years and be more reliable going forward. Parts are also readily available for this model and it has a seven year manufacturing warranty. Do members think this is a good combi boiler or are there others out there that are significantly better? Any advice would be gratefully received.
November 27, 2025Nov 27 1 hour ago, FlatMax said: I'm not looking for big efficiency savings here Why not when it's easy to do, actual boiler efficiency has little to do with boiler model more to do with how it's plumbed in and controlled. You could probably save a good 20% on heating costs. And get way better hot water performance. So choose your combi of choice, but make sure it's controlled via opentherm, not on off thermostats. But ideally has plenty of turndown so min output is low. 1 hour ago, FlatMax said: Baxi Duo Tec 28 i Not the best boiler out there, pretty poor turndown, with a min output of about 10kW, so boiler will cycle a lot at mild temperatures. The best will turn down to under 2kW. Can only run at a set flow temp. So not the most efficient by a long way. Hot water flow rate is 11.5L minute. Just looked at my old boiler and it did 15L minute at the same 35 Deg temp rise. And had a turn down to half the one you are looking at. I would look at other makes and models.
November 27, 2025Nov 27 I did the sane thing many years ago - had a glow worm boiler that had given sterling service so chose another glow worm the same KW rating - it was a big mistake!!!! I didn’t take into account insulation improvements to the house, SUDG, CWI improved Loft insulation etc boiler was massively oversized - couldn’t do DHWP, had a terrible modulation level 24 KW max 10 kW min and as a result cycled like a twat in shoulder seasons and wasn’t that great in the winter either find a better boiler as @JohnMo says - preferably with same pipework configuration and flue position and get some real benefits and savings with a better modulation
November 27, 2025Nov 27 Author 7 hours ago, JohnMo said: Not the best boiler out there, pretty poor turndown, with a min output of about 10kW, so boiler will cycle a lot at mild temperatures. The best will turn down to under 2kW. I hadn't even considered this; thanks for the insight. Here in South Devon we don't get much below 10 celsius ambient during the coldest months, so I can keep the house at 20C with a flow temp of 55C no problem. We have twenty rads in total (thirty five panels if you count the double rads) spread over three floors and 2,500 sq ft floor area. Building was new in 2003, so half decent insulation. What would you consider is a good turndown ratio for a modern condensing combi? Our old Baxi has a ratio of 3:1 which oddly, is the same as the latest Duo Tec 28! Thanks again.
November 27, 2025Nov 27 A big Viessmann combi A Vitodens 200-W has a 17:1 turndown, so you could install a 30+kW for great DHW performance and still it would tick away down to below 2kW when it's mild. Set the boiler to run WC mode and it would fire up alter flow temp automatically and boiler would run for long periods at best efficiency. Comes with up to 10 years warranty Atag make a good boiler, turndown isn't as good as Viessmann, but a solid machine.
November 27, 2025Nov 27 7 minutes ago, JohnMo said: A big Viessmann combi A Vitodens 200-W has a 17:1 turndown, so you could install a 30+kW for great DHW performance and still it would tick away down to below 2kW when it's mild. Set the boiler to run WC mode and it would fire up alter flow temp automatically and boiler would run for long periods at best efficiency. Comes with up to 10 years warranty Atag make a good boiler, turndown isn't as good as Viessmann, but a solid machine. ^ WHS beat me to it Valiant are catching up with their recent boiler so also worth consideration - their controls are also highly regarded Intergas are also in with a shout Whatever you go for find an installer that does specialises in the brand - boxt and other "box" movers are unlikely to get the best out of the install
November 28, 2025Nov 28 Author Thanks to everyone who has been kind enough to post their replies. I think I now have all the info required to make an informed choice. What I really need to do is find an installer with whom a reliable relationship can be established; we don't have that at the moment.
November 28, 2025Nov 28 Have a look for a Heat Geek installer in your area. They have been trained properly on low temperature heating systems etc. if you go on to the heat geek website there's a page for finding local installers
December 22, 2025Dec 22 Author **UPDATE** Following all the great advice kindly offered on here, I managed to establish a working relationship with a WB approved installer just a couple of miles away. The ageing Baxi 105e has been replaced with a WB Greenstar 4000 rated at 30kw for DHW/24kw for CH. I calculated the heat loss for the building at 12.5-15kw (it's a 2002 build of 340m2 set over three floors, with total volume of 1,120m3) at ambient of 5C and inside at 16C. We don't like the house too warm, so these metrics are fine for us. The boiler has a turndown ratio of 1-8, so 3kw up to 24kw is the operational output range. Before looking at weather compensation, I've been experimenting with simple inputs like range reduction, flow temperatures, and proper use of our existing TRVs; the system remains under the control of a Hive Mini on/off arrangement. The original twenty radiators were substantially over-sized when the house was built in 2002, so this will work in our favour for a 'long and low' regime. I've range rated the boiler down to 50% (12.5kw) and reduced the CH flow temp to 50C; I have also dropped the DHW to the same value and might go lower than this eventually. All the rads were balanced with the TRVs wide open and heat loss across the panel is around 10C. All the rads across the three floors heat up fairly evenly from cold, and after two hours the house is really very comfortable. The boiler's return temperature after two hours of heating is 44C and it's condensing really well; the amount of water it discharges is extraordinary. Now the fun bit for the techies on here. Having range rated the maximum CH output to 12.5kw, how come my Octopus smart meter says I'm using 20kw per hour of gas when the boiler is firing from cold? The half hourly plot does show the boiler modulating down a bit as the system heats up, but it's still using around 18kw each hour. The input to output ratio for the boiler is almost the same, so I am completely mystified. Am I wrong in believing that 12.5kw is the most the boiler can consume for CH?
December 22, 2025Dec 22 25 minutes ago, FlatMax said: ambient of 5C and inside at 16C Pretty flawed heat loss calculation you should have done it at -3 outside and 20 inside, but your boiler is still ok for that. Your just fooling yourself with overly small heat losses and too smaller range rating figure. Range rating to your calculations for heat losses at +5, what happens when you get a zero degree day, and your house drops to 11 degs? Because your boiler output is too low. Think I would rerun the heat loss calculation for realistic figures and range rated accordingly. 44 minutes ago, FlatMax said: from cold, and after two hours the house is really very comfortable First alarm bell is this. If you letting the house get cold (16 is cold in my book and that's your target temperature), the boiler needs to run balls out (especially when range rated right down), so may actually be struggling. Taking a long time to find a comfortable running point. To get a house to 16 with radiators in 2 hours is a long time. For me You have range rated too low You allow too much set back when heating is off - at a target of 16 why would you set back at all. Just let the heating run 24-7. Let everything stabilise. Your boiler will start to run more efficiently and modulate down on its own. Range rating is good for stop start heating as it allows a level of heating output more suited to the house at startup, but you have to careful, analogy If you are trying to fill a bucket with a hole in it (your heat loss), the hole allows 10L per minute to leak out. You open the tap (your boiler) and it flows at 10L per minute you will never fill the bucket. Open to 11L per minute it going to take a long time to fill. That is where you are now. Boiler running hard for too long.
December 22, 2025Dec 22 5 hours ago, FlatMax said: boiler is firing from cold The useful efficiency will be pretty poor initially as little condensing may be happening. The 12.5 kW you have limited to may only be a rough setting and is the thermal output. The efficiency may be down to 65% at start up, which is getting close to 20 kW. Or Was it heating water then?
December 22, 2025Dec 22 Author Thanks everyone; most helpful. So, @JohnMo I have re-rated the heat loss as per the scale shown by @marshian; it's Category three, pre-2006 new build. Using this chart gives 30-50w/m2 so between 10.5kw and 17kw plus 10% for on/off. If I take the mid-point then it's 15kw including the 10%, so I am too low at 12.5kw as @JohnMo says; I'm going to range rate it for 17kw and see what we get. Just as an aside, how quickly should the rads heat up to 50C if the boiler is correctly rated? Ours are taking about 45 minutes. (BTW @SteamyTea, there was no call for DHW when the CH was running) I'll post an update, but again many thanks for taking the time to respond to my query. Cheers.
December 22, 2025Dec 22 12 hours ago, FlatMax said: how come my Octopus smart meter says I'm using 20kw per hour of gas when the boiler is firing from cold? The half hourly plot does show the boiler modulating down a bit as the system heats up, but it's still using around 18kw each hour. The input to output ratio for the boiler is almost the same, so I am completely mystified. Am I wrong in believing that 12.5kw is the most the boiler can consume for CH? Octopus is measuring input gas rate, you are measuring/assuming output. There will always be a difference between these as your boiler will not run at 100% efficiency. With zero heating controls, efficiency of a modern boiler is assumed to be 89% in testing and depending on the whole system could be as low as 75% efficient.
December 22, 2025Dec 22 53 minutes ago, FlatMax said: says; I'm going to range rate it for 17kw and see what we get. I wouldn’t range rate it at all if heating to a schedule to start with but I’d assess the warm up time and consider range rating only if house heat up was very fast - even then I’d probably not bother with scheduled heating and that’s coming from someone who has range rated boilers in the past but only when they’ve been grossly oversized maybe monitor your gas usage over the winter period and look at it again with a bit of data from octopus (where you can get a massive amount of half hourly data)
December 22, 2025Dec 22 21 minutes ago, marshian said: maybe monitor your gas usage over the winter period and look at it again with a bit of data from octopus (where you can get a massive amount of half hourly data) Saturdays usage in graphical form But you can extract it in 30 min slots in excel format - once you have that you can use HDD data to get a very good picture of your heat loss if heating 24/7 - on a schedule it's not going to be as accurate but it'll give you a good guide PS the peak at 06:00 to 06:30 was my water heating slot Edited December 22, 2025Dec 22 by marshian Clarify the peak
January 2Jan 2 Author On 22/12/2025 at 21:02, marshian said: ......maybe monitor your gas usage over the winter period and look at it again with a bit of data from octopus (where you can get a massive amount of half hourly data) I think this is good advice so I will have a round up once we get into the warmer weather. Your usage figures for Saturday 20th December are like chalk and cheese compared to mine! Admittedly, our house is large at 340sqm (and 1,120cm volume) and It was a warm day for us here in South Devon. Even so, I used 45kWh for just four hours of scheduled heating in the morning whereas you used c55kWh for the whole day. The take-home message from your post is that I need to explore more fully load/weather compensation controls that can be used with the WB, so that its turndown output of 3kw can be more efficiently used. The problem as I see it (looking at the reviews in December 2025), is that all the weather compensation controls are somewhat unreliable, especially so the WB Easycontrol. I need a truly bomb-proof fit and forget system; at the moment I'm not seeing this in the trade reviews.
January 2Jan 2 11 minutes ago, FlatMax said: Saturday 20th December are like chalk and cheese compared to mine Don't get hung up, on yours compared to mine, it's meaningless. I would keep things simple first. Keep your on-off heating, bring down the CH flow temp first and extend your heating windows, so you slow the whole thing down. Plus don't switch off during the nighttime etc, just cut the target temp a couple of degrees. Trim 5 degs of flow temp every couple of days and see how it responds. Once house gets a little to cool, add a couple of degrees flow temp back on. But before you start, make sure any radiator valves or thermostats, are set to the same time periods, so everything works together. The above will get the boiler running very efficiently, it's simple and costs nothing and then gives to good starting place to understand how you house responds to different flow temperatures.
January 2Jan 2 10 hours ago, JohnMo said: Don't get hung up, on yours compared to mine, it's meaningless. I would keep things simple first. Keep your on-off heating, bring down the CH flow temp first and extend your heating windows, so you slow the whole thing down. Plus don't switch off during the nighttime etc, just cut the target temp a couple of degrees. Trim 5 degs of flow temp every couple of days and see how it responds. Once house gets a little to cool, add a couple of degrees flow temp back on. But before you start, make sure any radiator valves or thermostats, are set to the same time periods, so everything works together. The above will get the boiler running very efficiently, it's simple and costs nothing and then gives to good starting place to understand how you house responds to different flow temperatures. WHS ^ I did manual WC for nearly 2 years on scheduled heating - it worked quite well - not as good as WC but really only a few days a year when you really need to wind up the flow temps rest of the time a happy medium works well
January 2Jan 2 11 hours ago, FlatMax said: Your usage figures for Saturday 20th December are like chalk and cheese compared to mine! Admittedly, our house is large at 340sqm (and 1,120cm volume) and It was a warm day for us here in South Devon. Even so, I used 45kWh for just four hours of scheduled heating in the morning whereas you used c55kWh for the whole day. House is 1/3 of yours 113m2 however it is a stupid T shape with many rooms having 3 external walls which in a 1980’s house hurts. what I would say however is heating 24/7 with or without setbacks for me is actually not much of an increase on heating via a schedule with much higher flow temps for shorter periods morning and night - house temp swings were dramatic - far too easy to overheat the house and it never felt as comfortable as it does now. (Less than £50 a year from memory) what really triggered the move to 24/7 was that I would run the CH at the weekend all day and Monday would always be really low usage compared to the rest of the week - simple when I thought about it - I’d warmed up the internal fabric of the house over the weekend and on Mondays it gave it up again…..
Create an account or sign in to comment