Posted

Hello

Newbie to the site and looking for a bit of help/ guidance. 
Im currently refurbing my en suite, which involves the relocation of a radiator. 
I’ve drained the system (gravity fed) & relocated the pipes. 
Refilled the system, all rads working except downstairs lounge (most prob furthest from cylinder)

Ive tried all the usual stuff, bleeding, balancing but no joy. Lockshield & TRV all ok. 
Points to note-

There is no rad currently connected to the relocated pipes in the en suite & the un functioning rad (perhaps coincidentally ?) is the point where I drained the system from. 
Any ideas?!

With thanks 

Posted
14 minutes ago, Jon_S said:

no rad currently connected to the relocated pipes in the en suite & the un functioning rad (perhaps coincidentally

Most likely not a coincidence. With a missing radiator not sure how you rebalanced the system, depending on it's plumbed, suspect you have simply cut the flow to the radiator that doesn't work.

  • Thanks 1
Posted

Where the rad is missing, you need to bleed the air out of those tails.

 

If the problem then persists, turn the TRV of EVERY other rad 100% off and leave the rad not working 100% on, and run for 30 mins. 
 

Once (if) you see heat getting to the lazy rad, then open the rest of the TRVs back up and put the telly on. 

  • Like 1
  • Thanks 1