My proposed ASHP install is 12 metre run of 32mm from outside to under the stairs where the UFH manifold is. Then 16 metres of 22mm upstairs to the UVC.  7kw Vaillant Arotherm by the way.  Installers are saying the mismatch is an issue and the Vaillant needs 28mm anyway.  Do i have an issue ?

Posted
1 minute ago, Post and beam said:

My proposed ASHP install is 12 metre run of 32mm from outside to under the stairs where the UFH manifold is. Then 16 metres of 22mm upstairs to the UVC.  7kw Vaillant Arotherm by the way.  Installers are saying the mismatch is an issue and the Vaillant needs 28mm anyway.  Do i have an issue ?

Let them fit the 28mm throughout, as even a 300L cylinder has 1” BSP to 28mm connections so why not use them and have full use of the coil? It’ll perform better so where’s the harm. 
 

If it’s a smaller cylinder with factory 3/4” / 22mm connections then I’d challenge. 

Posted

The 32mm runs under the house and up though the block and beam to the manifold under the stairs. This is a 'fixture' now. Do you mean replace the 22mm from manifold to UVC  with 28mm Nick. Keith

Posted
33 minutes ago, Post and beam said:

12 metre run of 32mm from outside to under the stairs where the UFH manifold is. Then 16 metres of 22mm upstairs to the UVC

Suspect your 22mm will cause pump to run out of head for satisfactory flow to cylinder. Which would then need an additional pump for cylinder heating.