Hi All, I have been experiencing issues with intermittent heating over the last few weeks. Sometimes the central heating works fine and all radiators are hot, but other times it is much more intermittent (e.g. for the first 10-15 minutes the radiators are hot, but then they go slightly warm or cold... every now and again they will go hot again but not always during the heating cycle).

Boiler is a Riva Advance HE m110B.32sm/c, and has been in at least around 9 years going from the installation book (we have been here just over 7 years).

I have been observing the boiler for the past couple of weeks to try and figure out a pattern to this - there isn't anything that stands out to me.

I always make sure there is a call for heat and the boiler is actually on, and the temperature of the stat (works off a single Hive stat) is not met, and have tried this by bypassing the stat and using the manual switch on the diverter valve which controls the radiator central heating (there is also a valve controlling underfloor heating separately). I generally don't have them both scheduled together (UFH is connected to its own wiring centre back to a panel at the boiler with everything else so the CH and UFH can be controlled independently) as the UFH will be on first to warm the floor, then radiators on separate, but have found that if i run them both together the heat output from both often doesn't seem to be as good. For information, the UFH circuit covers around 60m² on the ground floor, then for the radiator circuit there is 2 radiators on the ground floor, 4 radiators on the first floor, and 1 radiator in the converted loft.

All radiators have been balanced, and when the system is working they all get hot throughout the full radiator (including the flow, and the cooler return).

I have fitted a magnetic filter on the return near the boiler and the system has had x400 in it for just over a week now, which i am checking / emptying every other day at least. It is picking up slight fragments and the water is starting to look a bit brown, but nothing significant - i will be leaving it in the system at least 2 weeks (up to 4 weeks as suggested) then will flush out the system using the mains filling loop going around 1 radiator at a time). This is more on the basis that previously there had been several older steel radiators which have been removed (only 1 older rad remaining), and in case other rads are sludged up anywhere to try help.

I wanted to see if anybody might have any thoughts or advice on what the issue might be with the heating system being great some days and not good at all others even though the boiler is on and looks to be firing up still, with no errors.

A few things i have checked and other observations:
- i have taken the pump apart to check this and it is clean and spins freely - when the boiler is on it feels like it is working when touching it, but is there anything i need to be checking?
- the micro switches on the diverter valve all appear to be clicking, and the pins on the valve pushing freely in/out - i am thinking of taking the valve out to change all washers etc. and grease / change parts as part of a maintenance kit, just to see if this makes any different.
- at times the boiler will fire up and maintain longer than others, and you can hear the water being pushed out to the radiators (with the front case panel off), and feel it as soon as it hits the nearest radiator. The flow pipe is hot, then once water has moved it gets cooler initially. Sometimes i have noticed that the flow pipe is cooler from the boiler, but the last say half half a metre of the return pipe directly to the boiler is very hot. I dont know if this is normal at all with a combi at times, or suggesting a pump or diverter issue?
- pressure in the system is fine (typically set around 1.25)
- there is never any errors showing or lock out
- i have not investigated the primary heat exchanger, but will be looking to get a plumber to service the boiler sometime soon
- DHW heat exchanger has been cleaned out - no issues with this, and no issues with the hot water at all
- possibly a minor observation or something which makes no difference; when looking through the manuals i have noticed that the bottom half of the boiler doesnt match that of the m110B.32sm/c (the pump and diverter valve look different on pictures, and on the parts lists from suppliers / websites), but the fan, air manifold etc. in the top half all match. The bottom part appears to be the same as the parts and picture listed in the m110.32sm/c manual.

I appreciate there's lots of information above, but would anybody happen to have any initial thoughts on what might be the issue before i get the plumber booked in? Any particular known / common faults with this boiler to be mindful of?

Any advice would be appreciated, and if any other information might help then let me know

many thanks in advance!

Posted

Appreciate the first post is quite long, but wanted to try and provide as much info as possible! 

 

Just some other observations:

 

- with heating on, and just 1 radiator on (fully open) at a time they get very hot (apart from 1 downstairs which i think may need cleaning) and the single radiator will stay hot for as long as the heating is on 

- i've found that generally the heating in the morning works better than on an evening (without reaching the stat temp) - this may have nothing to do with it, but just an observation

 

I am going to re-balance them again from scratch to see if this makes any difference 

Posted
49 minutes ago, Burkle said:

just 1 radiator on

How thermostats do you have?

Are they all timed at different times?

Posted

With the hot return, I would be inclined to change the pump and start there, if you are after a DIY process of elimination.

Beware though that Biasi are the cheapest boilers on the market and have never agreed to fit one as the first one I did in a rental never actually made it to the commissioning before it went back to the merchant (in favour of a Baxi). 
Repairs to these, if you manage to get any robust tech support (I failed here, it was dire) then parts and labour will quickly cost more than the value of the boiler. 
We had multiple different failures on switch on, with different led lights flashing in different patterns to identify the fault, but even Biasi couldn’t decipher what the boiler was trying to tell us. 

Posted

There is 1 stat for the radiator system, and then another stat for the underfloor heating controlling that separately, but we have the heating programmed so the ufh comes on for around 3 hours, then the radiators come on 30 mins or so after. The temp in the house very rarely hits the goal temperature (20 degrees) on the central heating stat. 

 

Thanks for your advice too Nickfromwales. 

Posted
43 minutes ago, Burkle said:

There is 1 stat for the radiator system, and then another stat for the underfloor heating controlling that separately, but we have the heating programmed so the ufh comes on for around 3 hours, then the radiators come on 30 mins or so after. The temp in the house very rarely hits the goal temperature (20 degrees) on the central heating stat. 

 

Thanks for your advice too Nickfromwales. 

Do you know the installation methodology of the UFH and thickness of insulation?

 

If the system is otherwise working A-OK, does it still not then get to 21o?

Posted

The ground floor part of the house with the ufh is newer and this area does get warmer. There is 100mm kingspan in the floor and walls and roof are all to the newer part L. This part of the house gets warm if the ufh has been on a few hours (as you'd expect with ufh). It's the older parts of the house with radiators which will never get to temp.... which isn't an issue, as 17-18 is warm enough, it's more the fact some days the rads get warm and some they don't (more so). 

 

Posted

As an example with the radiators - this morning all radiators had heat to them (not hot though), this evening only a couple upstairs are warm... stat has not reached temp, boiler is on and water temp reading 60-65, and ufh is not. Hot water works fine when demanded. 

Both ground floor rads are cold, no lockshields or trvs have been adjusted (all trvs set at top temp). The gf rad without a trv is cold, and lockshields open as before (not fully, but around 6-7 quarter turns, it is furthest away), and the bathroom towell rail is cold, only has lockshields and is the 2nd nearest to the boiler. 

Posted
On 26/01/2025 at 18:58, Burkle said:

As an example with the radiators - this morning all radiators had heat to them (not hot though), this evening only a couple upstairs are warm... stat has not reached temp, boiler is on and water temp reading 60-65, and ufh is not. Hot water works fine when demanded. 

Both ground floor rads are cold, no lockshields or trvs have been adjusted (all trvs set at top temp). The gf rad without a trv is cold, and lockshields open as before (not fully, but around 6-7 quarter turns, it is furthest away), and the bathroom towell rail is cold, only has lockshields and is the 2nd nearest to the boiler. 

 

 

Boiler is on a burn - pump is circulating - my question is where is the heat going if it's not going to the rads??

Posted

Pump replaced, diverter valve taken apart and all parts replaced and greased, dhw heat exchanger cleaned, Ch circuit flushed through, radiators valves replaced and rads flushed individually. 

Fired up boiler manually from diverter valve and worked great to start, but then same issue. Gets to heat quickly, but it seems to just stay at heat and flame goes out. Pump doesn't seem to be constantly pumping water round, but when it does you can feel the heat flush through the flow. 

Pipes in the boiler and diverter get very hot, as well as initial part of return from boiler until the water pumps away. 

Any ideas on what might be the issue? Pcb ? Hot water still works no issues at all 

Posted

Just an update - primary heat exchanger removed and cleaned through with spirit of salts solution - everything is back to being hot! Must have been a flow issue through the heat exchanger 