CCTs, separation, bypass, and all that guff


HughF

Recommended Posts

1 hour ago, JohnMo said:

Only thing I would have different is made the tees 28mm not 22mm. To get a step change in velocity at the tees.

Consider it done…. Nothing pressed yet and I’ve got 28 Ts in the bucket.

Link to comment
Share on other sites

45 minutes ago, John Carroll said:

What temperature are you running the UFH (flow) at and what total flow rate through the two loops and return temperature do you expect?. 

I’d need to check my calcs from loopcad, don’t recall them off the top of my head. 2.5l/min at 33 flow rings a bell.

 

16mm @ 150 ish centres in 100mm concrete, on 200 pir. 2 loops, 50m each. 15m2 floor area in a new extension.

Edited by HughF
  • Like 1
Link to comment
Share on other sites

Just put a plug into this and got it flowing…. It’s taking heat from the flow. But the loop temps aren’t coming up, is that normal? I’d have expected it to take as much flow as it can in order to satisfy the flow temperature, is that an incorrect expectation?

 

The pipes into/out of the manifold are hot/cold…. And there is some warmth to the flow, but it’s not rising above 22.

Link to comment
Share on other sites

23 minutes ago, JohnMo said:

If it's the first time heating it will take quite some time to get heat back to the manifold. You are heating a few tonnes of concrete.

Yep, I figured as much…. I think I had an incorrect assumption about how it blended the water, assuming that it would in fact feed water at the requested flow temp (I’ve set the dial to 33) until the return from the loop was at that temp. Instead it seems to be flowing quite cool. The heat must be going somewhere, the flow line is hot and the return from the manifold is cold.

Link to comment
Share on other sites

What temperature is the HW (from the HP) going to the mixer?, if its 45C then it should give a mixed flow of 33C if the index on the TMV is accurate, once the slab is heated up then you might expect a return of 25C/27C, a dT of maybe 6C to 8C, if the flowmeters are flowing 2.5LPM each then the UFH input will be 2.1 to 2.8kw.

Edited by John Carroll
Link to comment
Share on other sites

 

16 hours ago, HughF said:

But the loop temps aren’t coming up, is that normal?

Just seen you have an Ivar mixer, you need to adjust the mixer to suit your flow rates.

 

They are very adjustable, if you didn't get instructions with the manifold you can normally download them.

Link to comment
Share on other sites

7 minutes ago, JohnMo said:

 

Just seen you have an Ivar mixer, you need to adjust the mixer to suit your flow rates.

 

They are very adjustable, if you didn't get instructions with the manifold you can normally download them.

I’ll have a look and see what I can download. Some energy appears to be going into the floor, but I can’t get the flow temp into the loops above 26 ish.

Link to comment
Share on other sites

10 hours ago, John Carroll said:

What temperature is the HW (from the HP) going to the mixer?, if its 45C then it should give a mixed flow of 33C if the index on the TMV is accurate, once the slab is heated up then you might expect a return of 25C/27C, a dT of maybe 6C to 8C, if the flowmeters are flowing 2.5LPM each then the UFH input will be 2.1 to 2.8kw.

Varies between 38-50 depending on the weather comp.

Link to comment
Share on other sites

3 hours ago, John Carroll said:

Have you tried turning up the mixing valve setting until you achieve 33C, it should react fairly rapidly.

that’s what I was expecting, it to respond quickly to a demanded flow temp when being fed with a considerably higher flow temp than the mixer was calling for.
 

 

It seems completely disconnected from the flow temperature I see through the loop, which again is sitting at 27. Getting dT 3 between flow and return, and the floor is doing a nice job of keeping the extension warm, so I guess it’s working… it seems that no matter what I set the mixing valve to, it sits at 27.

Edited by HughF
Link to comment
Share on other sites

13 minutes ago, HughF said:

that’s what I was expecting, it to respond quickly to a demanded flow temp when being fed with a considerably higher flow temp than the mixer was calling for.
 

 

It seems completely disconnected from the flow temperature I see through the loop, which again is sitting at 27. Getting dT 3 between flow and return, and the floor is doing a nice job of keeping the extension warm, so I guess it’s working… it seems that no matter what I set the mixing valve to, it sits at 27.

I used a couple of different mixers last year, including Ivar, feeding from a buffer charged via WC, but I had to have the mixer flow turned down to minimum and still had the flow cooler than I really wanted.

 

One of the reasons, when I went heat pump, I removed the mixer and pump and added to my big pile of good but useless heating bits.

Link to comment
Share on other sites

24 minutes ago, HughF said:

that’s what I was expecting, it to respond quickly to a demanded flow temp when being fed with a considerably higher flow temp than the mixer was calling for.
 

 

It seems completely disconnected from the flow temperature I see through the loop, which again is sitting at 27. Getting dT 3 between flow and return, and the floor is doing a nice job of keeping the extension warm, so I guess it’s working… it seems that no matter what I set the mixing valve to, it sits at 27.

A dT of 2C with a assumed total flow of 5.0LPM = UFH output of 0.7kw.

Link to comment
Share on other sites

3 hours ago, HughF said:

that’s what I was expecting, it to respond quickly to a demanded flow temp when being fed with a considerably higher flow temp than the mixer was calling for.
 

 

It seems completely disconnected from the flow temperature I see through the loop, which again is sitting at 27. Getting dT 3 between flow and return, and the floor is doing a nice job of keeping the extension warm, so I guess it’s working… it seems that no matter what I set the mixing valve to, it sits at 27.

If you are getting 3C dT then UFH output is ~1.1kw, have you a link to the mixing valve, it seems to have a adjustable bypass (if like the one below)

there is only ~ 0.7LPM of hot water at 45C mixing with 4.3LPM of UFH return water at 23C so requires very tight control, you would require 1.0LPM mixing with 4.0LPM to get 33C mixed temperature.

image.thumb.png.db1be768fb1db87917a429d40543534b.png

 

Edited by John Carroll
Link to comment
Share on other sites

I’ll post up the user manual when I’m in front of my laptop… the ivar mixer does indeed have two internal bypass’ both of which are adjustable.

 

If it turns out I can heat the extension with only 27 degree flow then that’s all good, less losses all round. It would just be nice to have another pair of eyes looking over the manual with me. 
 

Appreciate everyone’s input on this.

Link to comment