AliMcLeod Posted October 11, 2023 Share Posted October 11, 2023 (edited) Hi, Does an AC coupled PV install with a 3.6kW inverter and a 5kW battery require a G98 or a G99 application? I originally thought it was G98 but installer is saying G99 (so will delay the install). Happy to wait for it, but just interested. Is it because it's AC coupled with a batter ? 3.6kW even though the inverted is 3.6kW? Edited October 11, 2023 by AliMcLeod Link to comment Share on other sites More sharing options...
JohnMo Posted October 11, 2023 Share Posted October 11, 2023 Depends if everything including the battery is all done with a single hybrid inverter, G98, as the system cannot export anymore than the inverter rating. If you have PV and battery with seperate inverters G99 as you can exceed the G98 limits. Link to comment Share on other sites More sharing options...
AliMcLeod Posted October 11, 2023 Author Share Posted October 11, 2023 It is a 3.6kW Solis String Inverter and separate 5kW Puredrive AC battery system. Link to comment Share on other sites More sharing options...
JohnMo Posted October 11, 2023 Share Posted October 11, 2023 So it requires G99 as per your installers statement Link to comment Share on other sites More sharing options...
AliMcLeod Posted October 11, 2023 Author Share Posted October 11, 2023 Thanks, that makes sense. Link to comment Share on other sites More sharing options...