John1001 Posted October 6, 2023 Share Posted October 6, 2023 Hi, I'm going to give self designing/installing a vent-axia kinetic unit myself a go. My house is a bungalow and fairly small so I figured the air flow calculations were easy enough to do: 1 Kitchen/diner (53m3) 13 l/s 1 Bathroom 8 l/s 1 Utility 8 l/s ------------ Extract 29 l/s Bedroom(double) 11 l/s Bedroom(double) 11 l/s Bedroom(single) 5.5 l/s Living room 4.8 l/s (based on room size) ------------ Supply 32.3 l/s I see everyone's supply and extract calculations from BPC etc on the forum match up exactly. What room's supply or extract do I adjust to get these to match? Thanks Link to comment Share on other sites More sharing options...
JohnMo Posted October 6, 2023 Share Posted October 6, 2023 You need your volume of the house in m3 divide that by 2 to 3 to get your overall flow rate in m3/hr. Just increase the extract rates to match the supply rates if required. But living room flow look too low, it will end up a stuffy room, it should at least be the same or more as a double bedroom. Link to comment Share on other sites More sharing options...
Conor Posted October 6, 2023 Share Posted October 6, 2023 I had to more than double the extract flow rates to balance the supply. Your unit will balance the fan speeds anyway. Link to comment Share on other sites More sharing options...
John1001 Posted October 6, 2023 Author Share Posted October 6, 2023 (edited) Thanks JohnMo > You need your volume of the house in m3 House Vol. is 244m3 > divide that by 2 to 3 to get your overall flow rate in m3/hr 244m2 / 2.5 = 97.6m3/hr Is that the minimum flow rate or the target flow rate? The calculations have the actual flow rate at 138.6m3/h Bedroom(double) 11 l/s Bedroom(double) 11 l/s Bedroom(single) 5.5 l/s Living room 11 l/s = 38.5l/s / 3.6 = 138.6m3/h So 97.6m3/hr is the flow rate based on the size of the house (from what you said "You need your volume of the house in m3 divide that by 2 to 3 to get your overall flow rate in m3/hr.") And 138.6m3/h is the required flow rate based on the regulations Does it matter that these are so different. I assume I want to be hitting the regulation flow rate either way EDIT Actually if I divide by 2 instead of 2.5 it is 122 m3/hr, much closer to 138.6m3/h. But what's the meaning behind that number "2 to 3" that I divided by? Edited October 6, 2023 by John1001 Link to comment Share on other sites More sharing options...
JohnMo Posted October 6, 2023 Share Posted October 6, 2023 24 minutes ago, John1001 said: But what's the meaning behind that number "2 to 3" that I divided by Give you one of the factors that affects flow rate. The other as you mentioned is 25 minutes ago, John1001 said: calculations have the actual flow rate at 138.6m3/h So you choose the higher of the two flow rates, to set the min flow rate. So you just need to increase extract to match supply and you have your target flow rates set. Link to comment Share on other sites More sharing options...