I'm trying here to improve my TT earthing arrangement. Soil isn't the best, this topsoil, heavy clay chalk. Every layer scattered with copious large flints. 

 

There was an old 3/8" dia 4' rod in. Replaced with a new 5/8" 4' rod and remade all the connections. Made naff all difference. I've now got 3 5/8", 4' rods in, spaced <1 rod's depth between each. I've tried coupling extra rods on in all 3 positions but I'm consistently hitting something 4" down so guessing that much be the chalk layer. Even tried an SDS adapter to hammer them in. The reading is better with 3 rods but it's messy!

 

I have now a 600x600mm ex DNO copper earth plate here that I'm going to bury. Came from someone's farm where they had an 11kVA trannie on two poles and the DNO moved it/the poles leaving the plate in the ground with the wire cut off.

 

2023-03-15_06-15-39

 

Main question is should I bury it horizontal or vertical?

 

Hopefully this weekend I'll get a hole dug and see exactly what I have ground wise.

Edited by Onoff
Link to comment
Share on other sites

1 hour ago, Onoff said:

Main question is should I bury it horizontal or vertical?

When I was doing my metal shed at the last place I found a website that showed all that sort of detail. Says it should be vertical.

 

https://www.mepits.com/tutorial/497/electrical/electrical-earthing-grounding

 

 

Edited by Gone West
  • Like 1
Link to comment
Share on other sites

6 hours ago, Gone West said:

When I was doing my metal shed at the last place I found a website that showed all that sort of detail. Says it should be vertical.

 

https://www.mepits.com/tutorial/497/electrical/electrical-earthing-grounding

 

 

 

Thanks. This too refers to the plate being set vertical but at a lesser depth than your link suggests.

 

https://www.electrical-installation.org/enwiki/Installation_and_measurements_of_earth_electrodes

Edited by Onoff
Link to comment
Share on other sites

Just to add, with 3 short rods slung in (and I do mean slung in, I was going to tidy it up but will just remove them if I go with the plate) I'm seeing 13.3 ohms earth loop impedance and 17A pfc (L - PE) to earth. Short video:

 

 

 

 

 

Edited by Onoff
Link to comment
Share on other sites