elite Posted February 20, 2023 Share Posted February 20, 2023 I'm about to prewire for an ASHP - most likely from Cool Energy For the control cable, they specify a 3 core cable, but don't specify a cable size, am I okay to go with 0.75mm SY as I assume this cable will have little or no load? Link to comment Share on other sites More sharing options...
markc Posted February 20, 2023 Share Posted February 20, 2023 0.75 will be more than sufficient for control 1 Link to comment Share on other sites More sharing options...
elite Posted February 20, 2023 Author Share Posted February 20, 2023 Brilliant - thanks Link to comment Share on other sites More sharing options...