MortarThePoint Posted February 3, 2023 Share Posted February 3, 2023 Our kitchen design has two side by side cooker hoods. Is there such a thing as an Inline Rectangular to Round 90 degree bend to put in the left hand hood as in the first image below or do I have to have them both bend/tee onto a straight run as in the second image. The blue circle is a soil pipe I have to get round and the dark brown lines are the wall surfaces of the kitchen. [NOTE: I accidentally started this thread in the wrong section so am stopping it there restarting it here] Link to comment Share on other sites More sharing options...
MortarThePoint Posted February 3, 2023 Author Share Posted February 3, 2023 @Nickfromwales Posted: Any of this get you out of the 💩? https://www.tlc-direct.co.uk/Main_Index/Ventilation_Index/Ducting_Flat_6/index.html Link to comment Share on other sites More sharing options...
MortarThePoint Posted February 3, 2023 Author Share Posted February 3, 2023 1 minute ago, MortarThePoint said: @Nickfromwales Posted: Any of this get you out of the 💩? https://www.tlc-direct.co.uk/Main_Index/Ventilation_Index/Ducting_Flat_6/index.html Thanks @Nickfromwales, I've seen those parts from other suppliers and I can't see an Inline Rectangule to Round Tee. I was think along the lines of a straight section of rectangular duct with a spigot in the bottom for a 150mm Round to join. I guess I join the two extractors in 150mm Round and then adapt to Rectangular instead. Any reason Rectangular can't be used on its side, so the 220 or 204 dimension is vertical? Link to comment Share on other sites More sharing options...
MortarThePoint Posted February 3, 2023 Author Share Posted February 3, 2023 Here's what it would look like using Rectangular ducting on its side: Passing from one of the extractors: 150mm Round Straight 600mm 150mm Round Bend 150mm Round Straight 200mm 150mm Round Tee 150mm Round to 204x60 Rectangular Spigot 204x60 Rectangular Straight 1450mm 204x60 Rectangular to 125mm Round Adaptor 125mm Round Straight 450mm 125mm Round Bend 125mm Round Straight 350mm 125mm Round Vent/Grating I read bends count as 1.2m equivalent. This has 4 bends so overall is equivalent to 8m straight length of 204x60 I'd guess. I've read it should be kept under 5m equivalent, but is there a building reg that needs satisfying? Link to comment Share on other sites More sharing options...
MortarThePoint Posted February 3, 2023 Author Share Posted February 3, 2023 Here's a comparison of ducting resistance per metre for different types. At 288m3/hr it works out as: 144m3/hr 288m3/hr 150mm Round 0.4Pa 1.9Pa 125mm Round 1.4Pa 3.9Pa 100mm Round 4.1Pa 14.3Pa 220x90 Rect 0.4Pa 2.0Pa 204x60 Rect 2.1Pa 7.8Pa 121x60 Rect 6.0Pa - 110x54 Rect 13.5Pa - http://www.nuaire.info/catalogue/Nuaire_Ducting_Specification_Guide.pdf Link to comment Share on other sites More sharing options...
MortarThePoint Posted February 3, 2023 Author Share Posted February 3, 2023 Using the values in that Nuaire PDF, the total resistance becomes: 150mm Round Straight 600mm 1.1 150mm Round Bend 16.6 150mm Round Straight 200mm 0.4 150mm Round Tee 14.5 150mm Round to 204x60 Rectangular Spigot 90est. <<<< 204x60 Rectangular Straight 1450mm 11.3 204x60 Rectangular to 125mm Round Adaptor 14.3 125mm Round Straight 450mm 1.8 125mm Round Bend 26.4 125mm Round Straight 350mm 1.4 125mm Round Vent/Grating ?? TOTAL: 177Pa @ 80l/s (288m3/h) Half of that is from the plenum (aka "150mm Round to 204x60 Rectangular Spigot") which you'd almost always have in a system using rectangular ducting. Link to comment Share on other sites More sharing options...
MortarThePoint Posted February 3, 2023 Author Share Posted February 3, 2023 (edited) ____________ ____________ ____________ From these, I'd guess 150mm Round to 204x60 Rectangular using a 150mm Round Bend and then Adapter would be about 30Pa @80l/s so much improved over the Plenum (~90Pa @ 80l/s) if space allows. Edited February 3, 2023 by MortarThePoint Link to comment Share on other sites More sharing options...
MortarThePoint Posted September 2, 2023 Author Share Posted September 2, 2023 (edited) Do Building Regs set out a minimum distance between an extractor fan exhaust and an openable window? I'd be surprised if there is as I see bathroom ones near windows all the time. Edited September 2, 2023 by MortarThePoint Link to comment Share on other sites More sharing options...