RCBO to inverter advice please


lakelandfolk

Recommended Posts

3 hours ago, Jenki said:

5KW is around 35amp on mains 240 voltage. 

Are you sure? AFAIK rule of thumb is 4 amp per kw so 5kw is circa20amp. Likely easily handled by 2.5mm cable over half a meter, but..... If youre going to increase the RCBO rating to 32amp, youll need to increase cable size. 

Edited by Dillsue
  • Like 1
Link to comment
Share on other sites

14 minutes ago, Dillsue said:

Are you sure? AFAIK rule of thumb is 4 amp per kw so 5kw is circa20amp. Likely easily handled by 2.5mm cable over half a meter, but..... If youre going to increase the RCBO rating to 32amp, youll need to increase cable size. 

NO. 🙊  not sure where I got 35A from.   so as you said it is around 20-22A cable is ok to 27A  

 

@lakelandfolk. Please ignore my brain fart above.. 

  • Like 1
Link to comment
Share on other sites

5kw is 21.7 amps at 230v or 20.8 amps at 240v. 
 

Assuming 2.5mm2 is twin and earth, this can take up to 27 amps if ref method C - clipped direct. 
 

You may be able to get a 25 amp RCBO for your consumer unit. Guessing someone will be wiring in the new inverter though, so why not let them deal with it?

  • Like 1