lakelandfolk Posted February 2, 2023 Share Posted February 2, 2023 Hello, planning to upgrade our 3 kW inverter to a 5 kW model. Existing connection to the CU is via 2.5mm cable, only 500mm long, and 20 amp RCBO. Do they need to be increased to cope with the 5kW load? Link to comment Share on other sites More sharing options...
Jenki Posted February 2, 2023 Share Posted February 2, 2023 5KW is around 35amp on mains 240 voltage. 2.5mm Sq cable can take around 25Amp load so yes to both. 1 Link to comment Share on other sites More sharing options...
lakelandfolk Posted February 2, 2023 Author Share Posted February 2, 2023 Thanks Jenki, so 4mm cable and 32a RCBO?? Link to comment Share on other sites More sharing options...
Dillsue Posted February 2, 2023 Share Posted February 2, 2023 (edited) 3 hours ago, Jenki said: 5KW is around 35amp on mains 240 voltage. Are you sure? AFAIK rule of thumb is 4 amp per kw so 5kw is circa20amp. Likely easily handled by 2.5mm cable over half a meter, but..... If youre going to increase the RCBO rating to 32amp, youll need to increase cable size. Edited February 2, 2023 by Dillsue 1 Link to comment Share on other sites More sharing options...
Jenki Posted February 2, 2023 Share Posted February 2, 2023 14 minutes ago, Dillsue said: Are you sure? AFAIK rule of thumb is 4 amp per kw so 5kw is circa20amp. Likely easily handled by 2.5mm cable over half a meter, but..... If youre going to increase the RCBO rating to 32amp, youll need to increase cable size. NO. 🙊 not sure where I got 35A from. so as you said it is around 20-22A cable is ok to 27A @lakelandfolk. Please ignore my brain fart above.. 1 Link to comment Share on other sites More sharing options...
lakelandfolk Posted February 2, 2023 Author Share Posted February 2, 2023 OK, thanks Link to comment Share on other sites More sharing options...
Mattg4321 Posted February 2, 2023 Share Posted February 2, 2023 5kw is 21.7 amps at 230v or 20.8 amps at 240v. Assuming 2.5mm2 is twin and earth, this can take up to 27 amps if ref method C - clipped direct. You may be able to get a 25 amp RCBO for your consumer unit. Guessing someone will be wiring in the new inverter though, so why not let them deal with it? 1 Link to comment Share on other sites More sharing options...