I am installing a 6KW ecodan PUZ ASHP.
Looking to 1st fix the main cable to the ASHP.
It is a run of about 12m with insulation on one side of cable only.
In the manual it says it says 'Outdoor unit input capacity Main switch (Breaker)' as 16 A and minimum 3 x 2.5mm cable.
Does that mean the earth needs to be 2.5mm? (assuming it is one of the 3 cores)
Part of me thinks I should just put in a 4mm cable but I don't want to over specify unnecessarily.
Any one got an opinion?
A 12m run of 2.5mm² Twin & Earth or SWA on a 16A breaker will be well within spec. No need to provide a 2.5mm earth.
If you use a 2.5mm² T&E the CPC will be 1.5mm² - this is fine, if you use SWA you could use 2 core and the armour or 3 core and a core for earth and armour.
Assuming this unit is outdoor, I would use SWA.
Edited by Carrerahill
Hadn't thought about this though I am hoping to get away without it since the isolator for the ASHP will be very close to the wall penetration so I presume I can get away with some suitable conduit.
You could, I would cost up the options though, by the time you put in suitable conduit, conduit glands & saddles you may find that ordering a length of 2 or 3 core SWA is about the same price and less hassle for the installing electrician as they just need to run in a cable, clip it and terminate it.  2.5mm SWA is not that expensive, you will get some saddles for 20p each and 2 glands for £5.
Alternatively, mount the isolator on the house and bring the cable in the back (properly sealed with a grommet) and then run a piece of SWA from the isolator to the ASHP assuming it is indeed close enough.