jfb Posted July 6, 2022 Share Posted July 6, 2022 I am installing a 6KW ecodan PUZ ASHP. Looking to 1st fix the main cable to the ASHP. It is a run of about 12m with insulation on one side of cable only. In the manual it says it says 'Outdoor unit input capacity Main switch (Breaker)' as 16 A and minimum 3 x 2.5mm cable. Does that mean the earth needs to be 2.5mm? (assuming it is one of the 3 cores) Part of me thinks I should just put in a 4mm cable but I don't want to over specify unnecessarily. Any one got an opinion? Link to comment Share on other sites More sharing options...
Carrerahill Posted July 6, 2022 Share Posted July 6, 2022 (edited) A 12m run of 2.5mm² Twin & Earth or SWA on a 16A breaker will be well within spec. No need to provide a 2.5mm earth. If you use a 2.5mm² T&E the CPC will be 1.5mm² - this is fine, if you use SWA you could use 2 core and the armour or 3 core and a core for earth and armour. Assuming this unit is outdoor, I would use SWA. Edited July 6, 2022 by Carrerahill Link to comment Share on other sites More sharing options...
jfb Posted July 7, 2022 Author Share Posted July 7, 2022 22 hours ago, Carrerahill said: Assuming this unit is outdoor, I would use SWA. Hadn't thought about this though I am hoping to get away without it since the isolator for the ASHP will be very close to the wall penetration so I presume I can get away with some suitable conduit. Link to comment Share on other sites More sharing options...
Carrerahill Posted July 7, 2022 Share Posted July 7, 2022 1 hour ago, jfb said: Hadn't thought about this though I am hoping to get away without it since the isolator for the ASHP will be very close to the wall penetration so I presume I can get away with some suitable conduit. You could, I would cost up the options though, by the time you put in suitable conduit, conduit glands & saddles you may find that ordering a length of 2 or 3 core SWA is about the same price and less hassle for the installing electrician as they just need to run in a cable, clip it and terminate it. 2.5mm SWA is not that expensive, you will get some saddles for 20p each and 2 glands for £5. Alternatively, mount the isolator on the house and bring the cable in the back (properly sealed with a grommet) and then run a piece of SWA from the isolator to the ASHP assuming it is indeed close enough. Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now