jfb Posted July 6, 2022 Posted July 6, 2022 I am installing a 6KW ecodan PUZ ASHP. Looking to 1st fix the main cable to the ASHP. It is a run of about 12m with insulation on one side of cable only. In the manual it says it says 'Outdoor unit input capacity Main switch (Breaker)' as 16 A and minimum 3 x 2.5mm cable. Does that mean the earth needs to be 2.5mm? (assuming it is one of the 3 cores) Part of me thinks I should just put in a 4mm cable but I don't want to over specify unnecessarily. Any one got an opinion?
Carrerahill Posted July 6, 2022 Posted July 6, 2022 (edited) A 12m run of 2.5mm² Twin & Earth or SWA on a 16A breaker will be well within spec. No need to provide a 2.5mm earth. If you use a 2.5mm² T&E the CPC will be 1.5mm² - this is fine, if you use SWA you could use 2 core and the armour or 3 core and a core for earth and armour. Assuming this unit is outdoor, I would use SWA. Edited July 6, 2022 by Carrerahill
jfb Posted July 7, 2022 Author Posted July 7, 2022 22 hours ago, Carrerahill said: Assuming this unit is outdoor, I would use SWA. Hadn't thought about this though I am hoping to get away without it since the isolator for the ASHP will be very close to the wall penetration so I presume I can get away with some suitable conduit.
Carrerahill Posted July 7, 2022 Posted July 7, 2022 1 hour ago, jfb said: Hadn't thought about this though I am hoping to get away without it since the isolator for the ASHP will be very close to the wall penetration so I presume I can get away with some suitable conduit. You could, I would cost up the options though, by the time you put in suitable conduit, conduit glands & saddles you may find that ordering a length of 2 or 3 core SWA is about the same price and less hassle for the installing electrician as they just need to run in a cable, clip it and terminate it. 2.5mm SWA is not that expensive, you will get some saddles for 20p each and 2 glands for £5. Alternatively, mount the isolator on the house and bring the cable in the back (properly sealed with a grommet) and then run a piece of SWA from the isolator to the ASHP assuming it is indeed close enough.
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now