August 28, 20215 yr I noticed that the manual for the 12kW ArothermPlus calls for 25A “type c/d fuse”, as well as type A RCD. c25 breakers aren’t very common (MK discontinued theirs some time ago for example) so wondering what others are doing here.
August 30, 20215 yr My Vaillant advanced installer used a Hager 32A RCBO. Works well and no issues. Hope that helps.
August 30, 20215 yr On 28/08/2021 at 22:37, J1mbo said: I noticed that the manual for the 12kW ArothermPlus calls for 25A “type c/d fuse”, as well as type A RCD. c25 breakers aren’t very common (MK discontinued theirs some time ago for example) so wondering what others are doing here. ebay is often helpful, indeed VERY helpful in this case https://www.ebay.co.uk/itm/124864933988?hash=item1d1287b064:g:fgsAAOSwEBdgMSf6 A job lot of MCB's for £16 including postage including four new in packet MK 25a type C I would go and snap that up very quickly. EDIT if you don't and it's still there in a few days I will probably buy it myself.
August 31, 20215 yr Author I don't know how you found that (I spent ages trying) but I thank you for it!