Hi Thank you for letting me join the forum. I have a problem with a Renewable heating system. The control panel is an FTC5 PAC IF063B-E
 

there is a ASHP for under floor and HW. We have an immersion for hot water too. 
 

recently the hot water has stopped working. The immersion doesn’t come on either. I’ve hard wired the the immersion and it does work so the problem is somewhere in the control. 
 

looking at the thermistors all give sensible temperatures other than TH1A which says -39. 
 

when using manual control all pumps work but they don’t come on otherwise using the timer. 
 

any suggestions of where to look to solve the problem. 

Edited by Parkcollege
Posted

Have you spoken the the supplier or Mitsubishi? I've head they are good for support (one reason why they are so popular)

Posted

Thank you- I did and they replied very quickly which was great but all they suggested was to turn it off and on. Which surprisingly I’d already tried, several times, but to no avail. Hopefully they’ll be able to give some more helpful Suggestions