Observations on need for heating upstairs
PhilT replied to Post and beam's topic in Air Source Heat Pumps (ASHP)
how do you operate your daily schedule; on all the time at one temp? Any set back? Any switch off for a period of time? -
It's the Czech Vaillant tables - this is a good resource to access and understand them https://energy-stats.uk/vaillant-arotherm-performance-data/#:~:text=The Czech tables give you,your system should be doing. Taking a simple example, for a nominal spec of -2°C / 7kW heat requirement, at 35°C flow temp, the 7kW model has a COP of 3.3 but the 10kW model has a COP of 4.0 - a 21% advantage. At those power levels, the 10kW compressor is revving at 50rps vs the 7kW compressor at 90rps (see my previous comment about how friction loss is affected by rotational speed compared to surface area). In answer to the other comment, I was trying to explain, rather poorly, that my heat pump is an 11.2kW model, but the power requirement at -2°C is only 6kW. The Mitsubishi data tables show a similar picture to Vaillant, in that the next size down (8.5kW) is less efficient at similar power levels.
- 43 replies
-
- mvhr
- ashp and dhw
-
(and 2 more)
Tagged with:
-
The data tables don't support this. For a house with a theoretical heat loss of 7kW at ΔT of 22°C, if you compare a 10kW Vaillant Arotherm+ with a 7kW version, the 10kW will give lower operating costs across a whole year, because it is so much more efficient during the coldest days, when energy use is at its highest. In the real world of (hopefully) common heat pump ownership this is likely to be even more relevant as the larger pump will be far more forgiving of less-than-optimal operation by non expert users during the coldest months of the year.
- 43 replies
-
- mvhr
- ashp and dhw
-
(and 2 more)
Tagged with:
-
The data tables published by Mitsubishi and Vaillant, as examples, an 11.2kW vs an 8.5kW Ecodan, or a 10kW vs a 7kW Vaillant Arotherm+, indicate that the extra efficiency of the larger, slower revving scroll compressors* outweighs any inefficiencies in warmer times, but why would there be any significant losses for modern oversized scroll compressors cycling at reasonable intervals of no more than once or twice per hour in the warmer months anyway? Long gone are the days of fixed speed reciprocating compressors. Isn't the oversized low modulation inefficiency paradigm something of an urban myth now? *(friction losses rise only in direct proportion to surface area, but rise exponentially with RPM)
- 43 replies
-
- mvhr
- ashp and dhw
-
(and 2 more)
Tagged with:
-
how many people will be living in this house? 5kW is too low to keep up with family hot water demand in a property of this size. I have an oversized heat pump (11kW vs 6kW at -3degC) and it's great, I never have to worry about not being warm or getting hot water quickly. My experience, backed up by the data tables, is that oversized heat pumps are no less efficient overall, and more efficient during the coldest periods like we have been having over the last few weeks. Some headroom is essential for all sorts of reasons especially those situations where a strong recovery is needed - defrosts, power cuts, all the family off work and school with the flu, and any other situation where you need extra warmth, or the house temperature drops significantly and you need a fast recovery.
- 43 replies
-
- 1
-
-
- mvhr
- ashp and dhw
-
(and 2 more)
Tagged with:
-
Out of interest why are you doing this? I can't see how this would save any significant amounts of money given your bill was already very low. What about recovery times - how often do you get power cuts and for how long? Impact on hot water heating time? Impact on defrost recovery time, headroom for other unexpected issues etc?
-
I've been using Octopus Cosy since they introduced 3 cheap rate windows. As far as I know it's the only one which "allows" you to have the fixed outgoing 15p/kWh for your PVs (correct me if I'm wrong I haven't checked recently). My Cosy rates went up by 10% from November because Octopus were losing money on it. My average variable cost before VAT for November was 18.5p/kWh. I have radiators and load shifting is minimal. low/std/high variable rates are p/kWh 13.38 27.29 40.93
-
Ecodan Fixed Flow Mode - Exceeding Flow Temp Setting
PhilT replied to BadgerBadger's topic in Air Source Heat Pumps (ASHP)
possibly the heat pump's minimum modulation level cannot get that low? What happens if you set it to 27? -
30 Year Old 8mm Microbore Circuit Changes
PhilT replied to PhilT's topic in Central Heating (Radiators)
Certainly worth considering now I know the top floor is mostly 15mm -
The figures vary a lot by manufacturer for example, at 35C the 10kW Vaillant Arotherm Plus SCOP is 5.03 vs the 7kW model at 4.36 (MCS test results). But my calcs look at this in a different way, by comparing an 11.2kW heat pump running comfortably within it's so-called "mid-range" capacity (c. 9kW ball park) vs the equivalent 8.5kW running flat out, at different ambient temps. So an over-sized heat pump could be more efficient or, at worst, no less efficient than the "perfect size" (for want of a better description).
-
Looking to upgrade to 15mm. I thought the 8mm microbore circuit was fed by manifolds, but removing the downstairs ceiling reveals instead a 15mm secondary circuit feeding short 8mm microbore feeds to the upstairs rads, and long 8mm microbore runs dropping down to the ground floor rads (see photo). This should make things easier because I won't have to hunt around for the manifolds, I can just leave the upstairs rad circuit as it is, run two new 22mm pipes dropping down from the primary circuit upstairs, just after the secondary circuit pump in the airing cupboard, and then connect new 15mm runs from the two central 22mm drop downs to the downstairs rads. Any issues with that approach?
-
The output ranges in that data table aren't exactly like for like, but it indicates that the larger unit is more efficient across the whole range of ambient temps, so a more cautious approach in selecting the 'next size up' should not significantly compromise efficiency and running costs.
-
It would seem that for modern scroll compressors, for a given range of output, a larger compressor is more efficient than a smaller one across the entire ambient temperature range. This is the Ecodan data table. The Vallant Arotherm+ shows a similar pattern when comparing the 10kW and 12kW to the 7kW model. Up front cost is obviously a consideration. 11.2 "Mid range " vs 8.5 "Max" @ 35°C In kW In kW Out kW Out kW COP COP 11.2 kW 8.5 kW 11.2 kW 8.5 kW 11.2 kW 8.5 kW % dIff. outside temp °C -15 2.7 3.4 6.7 7.3 2.5 2.15 16% -10 2.9 3.7 8.1 8.5 2.8 2.3 22% -7 3.0 3.6 9 8.8 3.05 2.45 24% 2 2.4 3.0 9 9.7 3.75 3.2 17% 7 1.9 2.3 9 10.5 4.8 4.55 5% 12 1.4 2.3 9 10.7 6.25 4.6 36% 15 1.3 2.3 9 11.5 7.05 4.9 44%
-
the counter argument is that at the coldest temps, for a given heat output, an oversized heat pump works more efficiently than undersized - manufacturer's data tables back that up. During the coldest days you could be using 10 x as much electricity as the mildest heating days. Think about the maths, for example, 10% more efficiency x 100kWh on the coldest days = a 10kWh saving, whereas 10% inefficiency x 10kWh on the mildest days means only a 1kWh loss.
-
Ecodan PUZ-WM112VAA requires a software update.
PhilT replied to Vinz86's topic in Air Source Heat Pumps (ASHP)
Mitsubishi sent someone out to do mine for no charge to update to the firmware via the outside unit. It has made a significant difference especially in October, much longer runs at lower temp/power consumption and better control of room temp around the target. I'm running in full auto (room temp) mode using the Mitsubishi room controller.