Further to my post, anyone seeking to use a six port valve to switch a heat pump between differnent destinations also needs to consider the pressure in the pipework as the valve effectively creates two seperate systems (with some common pipework that includes the heat pump). Normally a single expansion vessel would be used to accomodate the expansion and contraction of the circuit operating through the heat pump. While there is a single circuit, a single expansion vessel (if appropriately sized) will be fine, but using a six port valve would seem to need at least one appropriately-sized expansion vessel per seperate system.
The Johnson Controls valve lacks a seal at the OFF position that can be used for isolation, and this provides a degree of protection against over-pressure. In theory, this would allow any overpressure at the heat pump to be disippated to a expansion vessel in either of the two systems, but this only works when the valve is used to isolate the heat pump from both systems. For safety, I am inclined to add a third expansion vessel on the common piping to the heat pump.