Fancoil flow temperatures on a Heatpump?

Featured Replies

Hi all

Anybody here run Fan coils with their Heat pump?

I'm looking to install a fan coil to a heat pump for the purpose of size reduction compared to large radiators which I don't really have the space for. All the major brands marketing says they work great with heat pumps. However I'm confused on how they could work?

General advice is to run a heat pump on weather compensation, modulating flow temperatures etc. Looking on the Open heatpump monitor website shows that real life running data of many heat pumps are that many happily tick along at temps such as 27, 32, 34 degrees etc most of the winter season. Only ever getting up to the higher temperatures in the brief cold snaps.

Digging into fan coils it appears they all seem to have temperature probes on the inlets that only allow the fans to run when flow temperatures exceed 35 degrees. I think I found only one that was set to 32

So how do people realistically run fan coils on a weather compensated heat pump if the unit will only kick in on the very coldest days of the year? I know there might be a way to override and manually operate the fan but that seems like a bit of a pain to do on a regular basis. Considering how much these units cost.

My plan was to run the fan coil on an open loop system of UFH downstairs and a Fan coil in the loft room of a bungalow loft conversion.

Many thanks in advance for any advice or thoughts.

To size a fan coil you refer to the data sheets for a given flow temp and get the expected heat output. You match output to room heat loss.

Flow temp max is defined by the design you have above. So bigger fan coil can run lower flow temp for a given output. Smaller fan coil requires higher flow temp.

Min flow temperature, a temperature probe measures water flow temp and gives a permission for fan to operate. Cheap units this is a fixed flow temp, others you change the value in installer settings.

I would probably run a fixed flow temp of around 33-35 degs if you want the full flexibility of the fan coil sized correctly for the space. If you want WC on the UFH run a mixer driven by the ASHP.

My Ecovector units use the 35degrees. I have a proper ducted Daikin unit but haven’t found time to fit it yet. The ecovector is more a drop in Rad replacement with more capacity and noise. The Ducted unit requires a bit more design and control as per John above.

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.