September 15Sep 15 We’re about to pour our slab and we’re setting in floor drains to use for the shower. There is a separate 4” pipe coming up just for the shower, and I’ve got a 2” reducer to connect the floor drain straight into it. That 4” pipe goes down about 400mm, turns horizontal and will connect to the main stack outside the building. There will be further ventilation back up the stack. As it’s a 4” pipe will there be enough air flow that it doesn’t need a different vent, or should I run another 2” pipe over to a wall to connect to a vent?
September 15Sep 15 That's not going to need a separate vent as a 50mm bath waste can run 4m without venting and a shower runs much slower. If that was a WC sat on that 100mm pipe instead of the shower trap there would be no question. However, consider a) access for cleaning the trap and that bit of 50mm pipe plus b) the 100mm branch cannot connect to the main stack closer than 450mm from the invert of the rest bend at the base of the stack.
September 15Sep 15 Would you not prefer a 4" floor drain? I used one once fits straight inside 4"pipe. But yeh wouldn't need a vent.
October 31Oct 31 I agree with kandgmitchell on this one, I would not add a separate vent for a shower on that size of pipe either, especially with ventilation back up the stack as you described. The one thing I would check before the slab goes in is that you can still get at the trap for cleaning, as a shower trap under a slab is a pain once it is covered. A quick test with a bucket of water before you pour is worth it too, just to make sure it drains cleanly and the trap holds its seal.