What is the required U-value according to the last (2022) building regs for pitched roof for single storey extension?

 

Is it 0.15 or 0.13?

 

If it was 0.15 can this be achieved by fitting Knauf mineral wool 44 loft insulation 150mm thickness between the joist and 150mm above the joists?

 

Thanks

Posted

0.15

 

https://assets.publishing.service.gov.uk/media/69c122a6cfa346b9d4704a55/ADL1_2026.pdf

Table 3.2 Limiting U-values for new fabric elements in existing dwellings.

 

And in answer to the 2nd Q: It depends. You'd probably get sign-off from many BCOs on the basis that 0.3/0.044=6.818(R value) and 1/6.818 (U value) = 0.1466(W/m2K). However your description (

39 minutes ago, ab12 said:

150mm thickness between the joist and 150mm above the joists?

conjures up for me a picture of lots of timber to contain the 'above' bit. You can do an area-weighted U value calc (Part L always used to have a guide to doing so - I suspect it still does) by notionally 'lumping together' the timbers into 300 thick 'portions'. If, say, you end up with 2m2 of wood at 300 thick, then your U value calc is for (say, on a 20m2 roof) 18m2 of insulation, and 2m2 of wood. I suspect you could end up slightly over (worse than) the required U value, but possibly no-one will quibble. I have often done area-weighted U value calcs (for my own 'happiness') and I do not think I have ever been asked by a BCO to show them.

  • Like 1

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...