Jump to content

LG Therma V - how to monitor COP


Beef

Recommended Posts

I have a 16kW Therma V, installed in the summer. 

 

I'm happy enough with the result - house is warm, water is warm, but I can't see how I can tell/monitor what the COP is on the installation. 

 

I've looked through the control panel, and the app, but nothing stands out.

 

Is there a way to monitor the COP, or have I misunderstood a fundamental concept? 

 

Thanks in advance

Link to comment
Share on other sites

I'm sorry  but you can't do that either.  You can install measuring equipment that will determine your COP and thus your SCOP.  At the time my Therma V was installed it was a requirement for the heat pump to have a dedicated electricity meter so I can tell exactly how much electricity my heat pump uses - but I don't think that is done anymore.  And my EPC has a very inaccurate estimate of the heat and hot water requirements for my house so I can make an equally inaccurate estimate of my SCOP.

Link to comment
Share on other sites

7 hours ago, Beef said:

How do I determine the actual seasonal COP?

You can take a guess at it, but the only real way is

 

Install a heat meter in the water pipes from or too the heat pump, this will have tappings in to the flow and return to measure water temperature. This then calculates kW and logs the data, to give kWh. You then need an electric meter or two, depending on how power is derived for the package, any external pumps and if you use an immersion. All these numbers are logged instantaneously and calculated to give kW and kWh. They will also give CoP and rolling SCoP in the software.

 

SCoP, is function of running CoP and standby CoP. More time you spend on standby, the worse the SCoP. I can get a CoP of 6 when running at 7 degs outside, but spend quite awhile on standby also, so will end of with a daily CoP nearer 4. That's running full WC, but it's also a function of heat loss rate and heat pump over/under sizing. Lots of things at play.

 

Really look to get the system performing, so it keeps the house warm first, log what's happening so you understand what the heat pump does and doesn't do. If a thermostat is switching on off in the house, your system needs to tweaked.

 

 

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...