Jump to content

Service penetration for 3 phase in passivhaus


Barny

Recommended Posts

Hi

 

we are aiming for passivhaus certification and have 3 phase electric. Has anyone done this? What size ducting did I you use for the electric penetration through your foundations?

 

we have 150mm ducting for the cable to TBS but that seems large Togo through foundation. I know we need the insulation and airtight tape around the cable but still seems like 150mm is large.

 

many thanks

Link to comment
Share on other sites

Mine is in 100mm duct, through an insulated raft foundation, without any airtight tape.

 

The largest duct we have through the floor is the pre-insulated twin pipe duct for the ASHP, which is 150mm.

Link to comment
Share on other sites

22 minutes ago, Barny said:

Thanks Ian. Is that an insulated 100mm duct? Thanks

 

 

Not for power, water, comms etc. just the ASHP supply and return is insulated.

 

I used a rigid 100mm duct for power and did wrap the outside in a 20mm thick foam, where it was cast into the concrete floor. I did this with all ducts to reduce their chance of fracturing if they were ever knocked.

 

Grey rigid in the background close to the centre was for power and comms, blue flexi is water, black (long) flexi is for ASHP comms and the shorter larger black one that's taped up is the ASHP feed and return. Brown rigids are obviously waste.

 

image.thumb.png.a041947633b870661021885c5481f998.png

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...