Building Regs (Part H) states that a drainage field serving a STP (or septic tank) needs to be located at least 15m from any building. Does anyone know whether this refers to the distance from the ground floor external walls / foundations only, or does this guidance include the distance from any part of the building, specifically upper level cantilevers and protrusions?

Posted (edited)
8 hours ago, Temp said:

I couldn't find a reason why it's 15m written down anywhere.

At least I'm not the only one in that case 🙃. All I can think of is that the minimum specified separation distance is recommended to reduce the risk of subsidence from creating any overly dry areas next to foundations?

Edited by EViS
Posted (edited)

I asked on Quora and someone replied that the 15m distance came from BS 6297 which I've not seen. Apparently its to do with the risk of a flooded drainage field getting into the building causing a health hazard. So on that basis I would suggest you don't need to consider overhanging parts of the building.

 

The responder also reminded me that the Approved Documents aren't the law but represent one way of demonstrating compliance with the Building Regulations Act. So it's upto the BCO to determine if an alternative proposal also meets the Act. I would try explaining to the BCO  that your drainage field will be 15m from any part of the building that could be affected by the drainage area flooding which you understand to be the intent of this part of Approved Document H and BS 6297.

 

Ideally a drainage field would also be down slope from the building?

Edited by Temp
  • Like 1
Posted (edited)

That's a very thorough response, thank you. Interestingly, BS 6297 states "position as far away as is practical, consider prevailing wind direction. Recommended minimum: 7 m" from "habitable buildings". It does mention "health hazard or nuisance" but not directly in regards to the position of the field in relation to buildings.

Edited by EViS
  • 2 years later...
Posted

I HAVE JUST HAD A DRAINAGE FIELD REPLACED AS THE OLD ONE HAD FAILED AFTER 30 YEARS OF USE    AND ITS WITHIN THE 15 METRE RULE .

BUILDING CONTROL ARE DRAGGING THEIR FEET SIGNING OFF. WE LIVE IN NORTH WALES. THERE WERE NO OTHER ALTERNATIVES  BUT TO REPLACE THE FIELD WITHIN THE 15 METRES. MY NEIGHBOUR HAS HAD A WHOLE NEW SYSTEM INSTALLED DUE TO HIS SEPTIC TANK HAD COLLAPSED AND HE IS HAVING THE SAME PROBLEM WITH BUILDING CONTROL. BOTH PROPERTIES HAVE BEEN SOLD AND BUILDING CONTROL ARE

HOLDING UP SALES COMPLETION.

IS THERE ANYBODY OUT THERE WHO CAN HELP ME.

REGARDS

MIKE

 

 

 

Posted

Well you could try arguing paragraph 3) of Regulation 4 which states:

 

(3) Building work shall be carried out so that, after it has been completed—

(a)any building which is extended or to which a material alteration is made; or

(b)any building in, or in connection with, which a controlled service or fitting is provided, extended or materially altered; or

(c)any controlled service or fitting,

complies with the applicable requirements of Schedule 1 or, where it did not comply with any such requirement, is no more unsatisfactory in relation to that requirement than before the work was carried out. (my bold).

 

So basically you would be saying that this new field is no worse than the original and with little alternative as to location, you do actually comply with the regulations. Hopefully BC will see this as a convenient way of closing the matter and moving on.....