Some Loops wired to wrong zone


newhouse87

Recommended Posts

Hi, just looking for advice on how to sort my issue. Basically 2 rooms in particular don't heat up, sun and sitting rooms. I done a test other day and when i had kitchen/sun/sitting room stat on i finally got heat into sun room. So im guessing it has 3 loops, 2 turn on when that stat calls for heat actuator2/3 but now im thinking  actuator 4 is also meant for that room or actuator 1 from either kitchen or sitting room stat. Below is what actuator turns on with corresponding stat. To complicate things further im thinking sitting room has 3 loops too so maybe a loop from bedroom 1 is meant to be going to sitting room. People say loops are usually grouped so kitchen stat turning on1-5 on small manifold and actuator 4 on main manifold and sitting room turning on actuator 1/5 on main manifold doesn't follow this theory. Rest Any help appreciated.

so sun room 2/3

sitting room 1/5

kitchen1-5 small manifold 4 main

bedroome1 6/7

master 8/9/10

back bedroom 11

small back bed 12

A

Edited by newhouse87
Link to comment
Share on other sites

Hi and welcome @newhouse87

 

It sounds like your doing the right thing by testing - trial and error!

 

It's a process that requires patience to get right. Personally, I would turn on one room thermostat at a time and check which actuator reacts, which flow and return pipes at the manifold become hotter and which area of floor warms up. This can take some time.....

 

Only then can you be sure of what you have and then consider the remedy.

 

Good luck 

 

M

 