MVHR - ducts to unit - fall?

Featured Replies

Install wisdom needed please as I certainly lack it...

I have seen recommendations to have a fall on eg the pipe from the MVHR unit exhausting the air to the outside, but do I need to consider a 'fall' for the pipe delivering air from kitchen and bathrooms (ie warm and moist) into the unit? In case of condensation in the pipe? Or am I overthinking this and the moisture will stay as vapour until it hits the actual heat exchanger.

Reason for asking is that I have only a small tight space in which to install the unit, along with HWC, UFH reservoir etc. Proving to be a 3D challenge...

Regards

Glenn

13 hours ago, Glenn said:

Install wisdom needed please as I certainly lack it...

I have seen recommendations to have a fall on eg the pipe from the MVHR unit exhausting the air to the outside, but do I need to consider a 'fall' for the pipe delivering air from kitchen and bathrooms (ie warm and moist) into the unit? In case of condensation in the pipe? Or am I overthinking this and the moisture will stay as vapour until it hits the actual heat exchanger.

Reason for asking is that I have only a small tight space in which to install the unit, along with HWC, UFH reservoir etc. Proving to be a 3D challenge...

Regards

Glenn

No need to consider anything for the distribution ductwork, as that will just get damp ( moisture ) and then dry out again as the air keeps flowing after the shower etc has been turned off.

If the MVHR unit supply air vents are on a gable with driving rain then it may be a good idea to have the first connected pipe rising slightly, but I've not ever really given this detail any further thoughts on previous installs, and I am still in regular contact with the clients.

I'd say don't worry, but make sure all joints are made robustly / duct supported well etc, and use rigid insulated ducting to atmosphere. I'd also avoid the fleece type attenuators and use metal 'box' attenuators where possible ( if you are going to install something for sound / noise reduction ).

  • Author

Thank you Nick! That is reassuring - thought I was overthinking it.

 

I spent more of my time coming up with the best pipe layout around the house, most efficient manifold position etc - I should have prioritised a little better on how to best fit in these dirty great 125mm ducts to and from the actual MVHR unit...

 

Regards

Glenn

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.