Jump to content

Should I or shouldn't I go for MVHR?


Recommended Posts

So, is it possible to establish what the ACH @50pa is for my house from the air permeability figure of 1.42 m3(hm2).  I understand that you cannot just apply a conversion ratio to get the answer, but beyond that I'm lost.

 

Colin.

Link to comment
Share on other sites

10 minutes ago, pulhamdown said:

So, is it possible to establish what the ACH @50pa is for my house from the air permeability figure of 1.42 m3(hm2).  I understand that you cannot just apply a conversion ratio to get the answer, but beyond that I'm lost.

 

Colin.

 

 

If you have the actual air leakage test figure from the air test report, in m³/hr, then you can use that, together with the calculated internal volume of the house, to derive the ACH

Link to comment
Share on other sites

19 hours ago, JSHarris said:

 

 

If you have the actual air leakage test figure from the air test report, in m³/hr, then you can use that, together with the calculated internal volume of the house, to derive the ACH

I'm sure you can.  But how? 

Link to comment
Share on other sites

Just divide the measured air leakage rate in m³/hr by the volume of the house, in m³, and you should get the ACH figure.

 

For example, our house measured air leakage rate at 50 Pa was 199m³/hr, and the house internal volume is 462m³.  199m³/hr divided by 462m³ = 0.43 Air Changes per Hour (ACH).

Edited by JSHarris
typo
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...