I am currently investigating the use of an ASHP for our new house and came across this information following a visit from one ashp installer suggesting that 10mm plastic pipe to all radiators using a centrally located manifold was the best approach.

 

This is from John Cantor’s website and he has written a book for those on the ASHP journey. I have just made a purchase - https://heatpumps.co.uk/

 

I hope you find this useful information...

 

Potential perils of plastic pipe

A college tutor recently suggested to me that the current environment in the heating industry does not encourage analytical thinking.   Maybe I should therefore be less amazed when I come across plumbers who think copper and plastic pipe are interchangeable.

Before you think I am anti-plastic pipe… I am not. The right size plastic is absolutely fine.
Environmental considerations of the materal aside, a more direct issue is that of flow rate and pressure drops.  Bore size of plastic is considerably smaller than copper, and it seems that this is often overlooked.  If installers select plastic pipe instead of copper without checking the size correctly, this could have a negative effect on heat pump’s performance.
 
(If you drop-off to sleep ½ way through this – read the scenario at the end )
 
 
With respect to the materials of plastic and copper, it would appear that the total energy involved in mining and manufacturing copper is far greater than the total energy (including the crude oil to make the plastic) to manufacture plastic pipe.  Here is one site that discusses the topic  , though not necessarily without bias.
 
Another factor to consider, that mainly affects pipe runs to hot taps etc, is the heat capacity of the pipe material. Plastic has a relatively high specific heat, and the wall is thicker, but it’s light. The net thermal capacity of the two is fairly similar.
(The cold feel of copper is more to do with conductivity from the hand than heat capacity)
 
However, obvious factors aside, one of the biggest issues that could affect installations involving heat pumps relates to the internal bore diameter.  This could have a very noticeable effect on the energy-efficiency of the system.
 
All metric pipes are measured by their outside diameter. As can be seen, with common pipe sizes (outside diameters), equivalent plastic pipes have considerably smaller internal area to copper. This has a dramatic effect on flow characteristics.
 
 The graphs below illustrate examples of the relative internal dimensions of common pipes.
 
 
 pipe-diameters-1.jpg

pipe-areas-1.jpg
 
A brief note about smoothness – It seems a common belief that plastic is ‘smoother’ than copper, but the inner wall ‘smoothess’ of the two is about the same.  However, plastic can be one-piece with slow sweep bends. In a different sense of the word, this is certainly ‘smoother’ than copper with tight elbows.   Re inner surface, we can assume the two materials are about the same.
 
Whilst it is fairly easy to look-up the pressure drop resulting from a specific flow rate with a specific pipe, we can see from the 2nd graph at-a-glance the relative flow capacity since the cross sectional area loosely indicates flow capacity.
 
If a certain flow rate is required, then we can look-up the required pressure that is required across the pipe length (beginning of pipe to end of pipe length).  The internal bore must be chosen such that the circulation pump is not overly large and energy-wasteful.
 
fixed-flow-1.jpg
This graph shows the approximate pressure required to maintain a certain flow rate for one specific fixed length of pipe example.  As can be seen, the pressure drop along the example pipe varies very dramatically, so the wall thickness makes very big difference. 
In this example, we can see that a 15mm copper pipe could be used with a common central heating pump (shown at 3.6m head, 36kPa). However, if plastic were chosen, then one would need almost 9m head to achieve the required flow – far beyond the capability of normal circulators. On the other hand, if 22mm plastic were chosen, the pressure requirements would be only 1m head (10kPa) which is likely to achieve very low circulation pump energy.
 
In real life, we tend to have a pump connected to a pipe system, and the flow rate that results is dictate by the balance between the pressure produced by the pump and the ‘restriction’ of the entire pipe work circuit.
 
There is a common concern about the restriction caused by the inserts (stiffeners) needed at joints. These restrict the bore, but they are so short that the the affect on flow is much less than it may seem.
 
For our final graph, we consider a pipe circulating with a fixed-pressure electronic pump (Alpha etc)
 
fixed-pressure-1.jpg
The above graphs show relative changes in flow rate that would result from a fixed pressure. If the pipe chosen were too small, then a larger circulation pump may be needed in an attempt to compensate for the extra restriction caused by the small internal bore.
 
The point here is that by choosing plastic instead of copper of the same nominal size, the system could potentially suffer unless the sizing is checked. There is of course no problem using plastic if it’s the right diameter.  Indeed, 28mm plastic may be an ideal choice for the connections from a heat pump simply to minimise noise transmission.  The best final solution is often a mixture of both plastic and copper for a multitude of reasons.
 
All this emphasises how dramatically the wall-thickness affects flow rates and pump pressure requirements, but how does this translate into reduced COPs?
 
Scenario(based on something I observed on a barn conversion)
 
Let us consider a radiator at a far distance from the heat pump.  The flow-rate relates to the pressure drop, which relates directly to the pipe-run length, and of course, the required flow-rate relates to the room size (bigger the heat demand, the more flow required).  In this instance the room is large.
The default pipe size choice would be normal 15mm (outside diameter), but if the sums are done, it may become apparent that the choice should be between either 15mm copper or 22mm plastic. 
 
How could a pipe with too small bore affect the COP? 
 
Radiators should be balanced, in general by throttling valves (lockshield)  on smaller radiators, and those with shorter pipe runs. However, this is actually quite a difficult thing to achieve with a heat pump because the temperature difference (water inlet to water outlet) may only be 5 degrees (°C).  (It’s much easier to measure and adjust when the temperature differences are larger).
 
It is not ideal, or easy, to have to throttle most other radiators on a system, and there is the added risk of the circulation pump not being big enough to cope.
The likely result of any ‘restrictive’ pipe-runs would be a reduced flow rate to the radiator.  This would result in a considerable area (the bottom) of the radiator being cool, and a reduced heat output to that room.
The obvious action to redress the short-fall of heat would be to increase the flow temperature by increasing the heating curve setting of the heat pump. i.e. increasing the flow temperate from say 40 to 45°C.    Now the heat pump has to heat ALL water to a 5 degrees higher level.  This is likely to reduce the COP by 10 to 12%.
 
This all indicates that one must never assume copper and plastic are interchangeable without considering the pressure drops and diameters.  That aside, we have also highlighted the importance radiator balancing.  Ideally the pipe runs to radiators would be laid out, and bore sizes chosen so that the flow rates are naturally about right without the need for much valve adjustment.  A little extra work on the design makes life much easier thereafter.

 

Anyone intersting in further reading on water flows – this site is very intersting
http://www.johnhearfield.com/Water/Water_in_pipes.htm

Here you can enter pipe sizes and find out the pressure requirements to achieve a certain flow rates.
  • Like 2