Spent the evening taping the vcl & just finished off the evening doing some heat loss calcs and the calc surprised me.
Background:
Ceiling u value 0.09
Walls 0.15
Glazing 1.4
Timber frame, well sealed I'd say.
Floor area 16m2 with volume of 41m3 (it is a high ceiling)
MVHR.
My calc suggests fabric heat loss of 180watts with the ventilation losses of 620watts. I assumed 2 airchanges an hour with -1 outside and 21 target, these two factors are responsible for the ventilation heat losses so are they reasonable assumptions? The calcs work out at a heat loss of 51w/m2 of floor area.
I'm being rather ocd with taping etc so I'm hoping for a good airtest so if I achieve between 1 and 2 air changes an hour. I havent allowed for the mvhr or any heat rising from below (floors will have sound insulation which will reduce the heat rising from below).
So do I need to suck it up or are some of my assumptions out?
Thanks,
CC