Thanks.
All of the suggestions have been considered and have either been tackled, or cannot be tackled:
- the radiators have been balanced, the problem remains.
- the system was flushed when the ASHP was installed. But, it is an old system. Crud may remain.
- the pipework is a mix of 22mm and 15mm pipework, but it missing much insulation under the suspended wooden floor. Getting to it is impossible as it would require lifting the Amtico, hence my thought to lay new pipes running direct from a manifold.
- I have a decent IR thermometer and am monitoring the flow/return at the ASHP. The issue is the overall flow.
I am wondering if the biggest issue seem is the poor overall flow. I would expect that a heating system would have a flow of 20+ l/m, the pumps are running consuming 54W and there is 6m of head, but only shifting 10-12 l/m. Surely this is a problem?
With an ASHP the flow is critical, I ideally want to get 2 l/m though every one of the 12 radiators in the house. Eg with a 42C flow and 38C return. You need to have a high flow rate, so that the difference between the flow and return can be minimised, allowing to to reduce the flow temperature and increase the COP.