  1. i think there are different ways of dealing with your situation in respect of the current permission.... however, it may not be so simple as getting what you want from it. Without seeing the permission or the details of the condition its difficult to say what the chance might be of changing anything through an application. An element of the decision may have come down to opinion, but there will also be planning policies to consider (national, district and potentially local), as well as any other constraints (conservation area? effect on setting of historic buildings?). Turning to an appeal, this again will very much depend on the reasoning for the condition. Very difficult to advise without knowing the full details and the context. With regards to conditions, as mentioned previously in this thread they will be worded very specifically to what you need to do - what stage they need discharging by; whether they need discharging or are just informative There are lots of examples of conditions and such like slipping the net and not being complied with then nobody ever noticing or enforcing. You just have to consider the worst case examples - we often have issues with people trying to sell their property, but their buyers solicitors or lender flag up that conditions are not discharged or permissions are not in place. Alot of the time this means losing sales or applying retrospectively. In your case if the aspect in question is quite obvious then it may not be so easy... also consider you home insurance policies and what terms and conditions suggest in these (there will be something regarding planning and building control permissions)
  2. Just a brief update on things again - since sunday and stripping the parts down again and putting everything back (old diverter and pins, new washers; old pump; new/refurbished heat exchanger) hot water has been fine still, no noise from boiler, and heating has worked perfect morning and evening every day except tuesday evening and wednesday morning (when the ufh had warmed up but not to the same extent, and radiators warmed for first few minutes only then nothing with boiler still on and water at temp). As above points, probably points to electrical / PCB issue, possibly still flow issue (although i cant see it being a blockage moving about unless its in the boiler as it would effect flow on both)... still no pattern to it! Waiting for boiler quotes. I just dont like not knowing why something just doesnt work properly anymore!
  3. CH and UFH both worked no issues this morning. Only obaervation I have from the diverter valve is that some of the pins in the diverter kit where slightly longer than the older ones. The older ones may have worn slightly and the system become accustomed to this over time, then the subtle change with the newer ones cause whining with the water pushing through. Still looking to replace, but just in case anybody ever gets a similar issue
  4. Just to add, there is constant power to the pump on this too when I've sat checking, it doesn't stop during operation
  5. There is the current 2 port valve (the snug lite) for the ufh on the flow, then the CH circuit valve under the boiler on the flow after the t off to the ufh flow.... so if i read correct, ideally the 2 port valve on the ufh circuit would be between the close coupled t's (open with ufh all the time), and would be closed if both the CH and UFH are on... that way there will be a circuit to the CH open at the same time the UFH is on a loop, but if only the UFH is on then there is a bypass on with this. As you can see there isn't space for this, and the manifold can't move, but might there be anything to help this with the current ABV set up? Obviously currently the ABV is there whether the UFH is on or the CH or both, and I presume in reality the setting of the ABV would be different if you treat both individually. Sorry for all the questions! I have a basic understanding of how the circuits can and would work, however I don't have the experience of it! If I am replacing the boiler I'd like to try and ensure the system is going to function. Just as a side note (whilst I'm waiting on people to see and quote for boiler replacement), I've stripped down the diverter valve again and put all the old parts back in but cleaned up with the washers from the newer parts. There is no longer any whining / whistling, and the CH seems to be working OK (albeit, the system still needs balancing properly since all rad valves got replaced). However, the UFH circuit now cuts the boiler after around 10 minutes with either safety stat fault or primary circuit fault. I've tried increasing the UFH pump speed and decreasing it but both seem to be the same. The water gets through as the manifold gets warm. It's presumably a flow issue, and another reason for trying to ensure the actual circuit is OK before just replacing the boiler
  6. These photos show the current arrangement under the boiler upstairs with the ABV, and then the arrangement at the manifold downstairs
  7. I will have a proper look when I'm home, but not sure there will be enough space available where the pipes have been dropped down in a corner. Might be able to make a primary flow circuit in the first floor under floor boards before they drop down as secondary (secondary flow pipes are going to be around 3m away though then).
  8. Something like figure 3 in this image thank you for a thorough explanation of everything too!
  9. It does have one out from the diverter back to the back of the return / pressure release valve, and it often gets too hot to touch
  10. It never used to do it before the diverter and pump where worked on, that's what puzzles me
  11. Hi sharpener, yes there is an ABV between the flow and return after the ufh was installed over a year ago. No flow through the ABV when it is whining though, and no change in the whining
  12. Thanks sharpener, and thanks Nickfromwales, i will check have a check on the wires during operation with a fluke pen to see if this is similar to what you found. I dont disagree with you on replacing the boiler, that is the next port of call! Labour thankfully hasnt cost anything in monetary terms (just my time!), and parts have all been reconditioned as they are generally now available new on this so its not been any more than £150 to date.... which it would likely have cost me more in getting somebody out to try and find the fault in the end anyway. I am just the sort of person who likes to understand how things work, and try and understand if it doesnt and why! Hence why all of this advice is great, but also shows that every situation can be different even if you can understand the workings. In the process at least i've flushed the system and all the radiators valves have been changed! The aspect i cant figure out so much still though is why the boiler is whistling / whining (sounds like the pump, but could be something else) only when the ufh is on / open and not when the CH is on or hot water. The pressure on the gauge for both the manifold and the boiler remain constant, and the ufh manifold shows there is flow during this. I did put the old pump head back on last night to see if this changed anything, but it still whistled. I also changed to the old pump body with the newer pump head to see if this made a difference but it didnt. It never used to make this noise, so that makes me wonder whether its the diverter valve which has had the insides replaced at the same time as the pump is the issue with the noise. In the process of speaking to a gas engineer on a replacement boiler
  13. Just to note - i have a similar topic in the Radiators Section - the below is a further summary follow this now the ufh has issues. To run through briefly what has been carried out: - all radiators valves (TRVs and lockshields) changed - x400 in system for 4 weeks and heating run as best as it would - central heating pipework main flushed (2 radiators removed and flushed individually) and the ufh heating loops (4 loops) mains flushed - all run through fine - boiler pump replaced - diverter valve pins / washers replaced and greased - dhw water heat exchanger cleaned out (no issues at any time with hot water anyway) - temp sensors replaced along with actuator motor on the combi 3 way valve in the boiler - primary heat exchanger removed and flushed through; has now also been replaced along with seals to chamber The main issue is the heating does not get hot. There seems to be flow in the system as you can hear and feel water going through, and on the ufh you can see there is flow. Initially on calling for heat with the radiators they will get warm, then the burner will go off and pump still seems to be working and water flowing but it is colder. After removing the primary heat exchanger, cleaning this, then reinstalling, the ufh worked like a dream again!.... but only for 1 night, then the day after everything the same - hence why the primary heat exchanger has now been replaced suspecting the old one just may have had too much limescale and the like lodged in it. After replacing the heat exchanger, initially the radiators all worked great for an hour or so, similar to when the old one was cleaned.... then back to how it was before. Boiler fires on calling on either the UFH or central heating - diverter valves on both open up fine and seem to have no issue. Since changing the pump (for the same model / type ) the pump does whine / whistle when the ufh is on and the boiler is firing, but this goes off when the central heating is on with it at the same time, and the mixer valve at the manifold also whistles (the only way to stop it is turn the mixer down to minimum... but then the temp is just cool water). When feeling the pipework you can feel when the hot water pumps out the boiler, but there are several minutes between this happening, sometimes even say 5-10 minutes, and then it is just a flush of hot water. As the hot water works with no issues at all i am trying to find what the issue is before i make the decision to replace the boiler. Any thoughts or advice would be much appreciated.
  14. Just an update - primary heat exchanger removed and cleaned through with spirit of salts solution - everything is back to being hot! Must have been a flow issue through the heat exchanger
  15. Pump replaced, diverter valve taken apart and all parts replaced and greased, dhw heat exchanger cleaned, Ch circuit flushed through, radiators valves replaced and rads flushed individually. Fired up boiler manually from diverter valve and worked great to start, but then same issue. Gets to heat quickly, but it seems to just stay at heat and flame goes out. Pump doesn't seem to be constantly pumping water round, but when it does you can feel the heat flush through the flow. Pipes in the boiler and diverter get very hot, as well as initial part of return from boiler until the water pumps away. Any ideas on what might be the issue? Pcb ? Hot water still works no issues at all
  16. As an example with the radiators - this morning all radiators had heat to them (not hot though), this evening only a couple upstairs are warm... stat has not reached temp, boiler is on and water temp reading 60-65, and ufh is not. Hot water works fine when demanded. Both ground floor rads are cold, no lockshields or trvs have been adjusted (all trvs set at top temp). The gf rad without a trv is cold, and lockshields open as before (not fully, but around 6-7 quarter turns, it is furthest away), and the bathroom towell rail is cold, only has lockshields and is the 2nd nearest to the boiler.
  17. The ground floor part of the house with the ufh is newer and this area does get warmer. There is 100mm kingspan in the floor and walls and roof are all to the newer part L. This part of the house gets warm if the ufh has been on a few hours (as you'd expect with ufh). It's the older parts of the house with radiators which will never get to temp.... which isn't an issue, as 17-18 is warm enough, it's more the fact some days the rads get warm and some they don't (more so).
  18. There is 1 stat for the radiator system, and then another stat for the underfloor heating controlling that separately, but we have the heating programmed so the ufh comes on for around 3 hours, then the radiators come on 30 mins or so after. The temp in the house very rarely hits the goal temperature (20 degrees) on the central heating stat. Thanks for your advice too Nickfromwales.
  19. Appreciate the first post is quite long, but wanted to try and provide as much info as possible! Just some other observations: - with heating on, and just 1 radiator on (fully open) at a time they get very hot (apart from 1 downstairs which i think may need cleaning) and the single radiator will stay hot for as long as the heating is on - i've found that generally the heating in the morning works better than on an evening (without reaching the stat temp) - this may have nothing to do with it, but just an observation I am going to re-balance them again from scratch to see if this makes any difference
  20. Hi All, I have been experiencing issues with intermittent heating over the last few weeks. Sometimes the central heating works fine and all radiators are hot, but other times it is much more intermittent (e.g. for the first 10-15 minutes the radiators are hot, but then they go slightly warm or cold... every now and again they will go hot again but not always during the heating cycle). Boiler is a Riva Advance HE m110B.32sm/c, and has been in at least around 9 years going from the installation book (we have been here just over 7 years). I have been observing the boiler for the past couple of weeks to try and figure out a pattern to this - there isn't anything that stands out to me. I always make sure there is a call for heat and the boiler is actually on, and the temperature of the stat (works off a single Hive stat) is not met, and have tried this by bypassing the stat and using the manual switch on the diverter valve which controls the radiator central heating (there is also a valve controlling underfloor heating separately). I generally don't have them both scheduled together (UFH is connected to its own wiring centre back to a panel at the boiler with everything else so the CH and UFH can be controlled independently) as the UFH will be on first to warm the floor, then radiators on separate, but have found that if i run them both together the heat output from both often doesn't seem to be as good. For information, the UFH circuit covers around 60m² on the ground floor, then for the radiator circuit there is 2 radiators on the ground floor, 4 radiators on the first floor, and 1 radiator in the converted loft. All radiators have been balanced, and when the system is working they all get hot throughout the full radiator (including the flow, and the cooler return). I have fitted a magnetic filter on the return near the boiler and the system has had x400 in it for just over a week now, which i am checking / emptying every other day at least. It is picking up slight fragments and the water is starting to look a bit brown, but nothing significant - i will be leaving it in the system at least 2 weeks (up to 4 weeks as suggested) then will flush out the system using the mains filling loop going around 1 radiator at a time). This is more on the basis that previously there had been several older steel radiators which have been removed (only 1 older rad remaining), and in case other rads are sludged up anywhere to try help. I wanted to see if anybody might have any thoughts or advice on what the issue might be with the heating system being great some days and not good at all others even though the boiler is on and looks to be firing up still, with no errors. A few things i have checked and other observations: - i have taken the pump apart to check this and it is clean and spins freely - when the boiler is on it feels like it is working when touching it, but is there anything i need to be checking? - the micro switches on the diverter valve all appear to be clicking, and the pins on the valve pushing freely in/out - i am thinking of taking the valve out to change all washers etc. and grease / change parts as part of a maintenance kit, just to see if this makes any different. - at times the boiler will fire up and maintain longer than others, and you can hear the water being pushed out to the radiators (with the front case panel off), and feel it as soon as it hits the nearest radiator. The flow pipe is hot, then once water has moved it gets cooler initially. Sometimes i have noticed that the flow pipe is cooler from the boiler, but the last say half half a metre of the return pipe directly to the boiler is very hot. I dont know if this is normal at all with a combi at times, or suggesting a pump or diverter issue? - pressure in the system is fine (typically set around 1.25) - there is never any errors showing or lock out - i have not investigated the primary heat exchanger, but will be looking to get a plumber to service the boiler sometime soon - DHW heat exchanger has been cleaned out - no issues with this, and no issues with the hot water at all - possibly a minor observation or something which makes no difference; when looking through the manuals i have noticed that the bottom half of the boiler doesnt match that of the m110B.32sm/c (the pump and diverter valve look different on pictures, and on the parts lists from suppliers / websites), but the fan, air manifold etc. in the top half all match. The bottom part appears to be the same as the parts and picture listed in the m110.32sm/c manual. I appreciate there's lots of information above, but would anybody happen to have any initial thoughts on what might be the issue before i get the plumber booked in? Any particular known / common faults with this boiler to be mindful of? Any advice would be appreciated, and if any other information might help then let me know many thanks in advance!
  21. Update - Andehh, it has always done this, but hasn't been used much since being installed and has never has a pattern to it. However, I've not had any issues for a good few days now. I've tried a few things since my original message, but the latest thing I have done is move an existing hub upstairs (a hub for electric car charger). Never thought too much of it... until I've notices that the tv remote for the tv upstairs nearest this hub no longer works... I'm suspecting this may be the issue!
  22. Just another update - tried changing to different channels and resetting everything again, it's worked then lost connection again until power reset... tried moving stat to different areas.. same scenario, sometimes within half a day it'll lose connection, sometimes a few days. Other than that these stats and centre just don't like it here, I cannot figure it out. No pattern to it losing connection tion at all, and the only way it will regain is to shut power off and on (have to leave it off for 20-30 seconds too). Even if the stat calls for heat but the ufh doesn't fire up, if I leave the stat on the schedule, then re-power the wiring centre, it gains connection and fires up fine. If anyone has any ideas as to how the power might effect the wiring centre antenna let me know. I think I will look to replace the stats with hives to see if these experience the same issue
  23. a bit of an update - system has been working fine generally coming on and turning off (if needed depending on temperature) since putting everything onto a single stat.... until this morning! Heating did not initiate on the wiring centre, but shows as being turned on on the stat (flame symbol). I downloaded a wifi analyser and have checked this to see if any signals are conflicting, but i've never seen anything on the app which looks like it could be that stat signal (only wifi internet services around the area). I am going to try the stats on a different channel to see if this makes any difference too, and will try and change this without powering down the system first to see if it switches over. I will keep you updated
  24. Thanks Temp, i will look into this and try pairing the stats to the receiver is no problem, and i've treid a couple of different channels on here to see if it made a difference, but i will see if i can find whether there is any conflict first too
  25. Not as far as i am aware with the way everything is scheduled, and no noticeable increase in gas usage / bills (other than the fact they keep going up!). The schedule on the stats for both the radiators and the UFH are all set to the same temperatures, during the same time periods. We also don't have the temp set too high on the stats either (typically 17 degrees when heating required, and this would typically be for around 4 hours per day in cold weather), and also find the boiler temp setting doesn't need to be too high (typically around 50-55) - this is just what we are used to living in and anything warmer gets too hot. If we need extra heat with either use the boost functions (which is then when the boiler might be used for just 1 zone), or put the burner / fire on. Whilst the heating is on if the zone with the radiators gets to temp quicker than the UFH zone area of the house then the stats shuts off the port valve for that part of the system but may keep running for the other.
×
×