My flat has an old SSE THTC setup. Basically one meter (on the right) feeds the top CU (both are metal) which covers all the sockets, lights etc.
The Radio Teleswitch on the left supplies permenant power to the water heater and 4 convectors. There is also a permenant supply to a Heater Boost button for heating up hot water quicker.
The Teleswitch also tops up at various times 3 storage heaters.
So, 4 different live feeds.
I recently had an EICR done, it has been given a C2 (521.5.1) because there is one neutral which goes through from the meter box onto a Henley block and then 4 feeds into the CU in the top. Thus live and neutrals not going through the same holes, classed as a C2 as the lives come in through the rear of the CUs.
To sort this I suspect the Henley block will have to go back to the meter box and the 4 neutrals then follow the live cables in through the rear of the CU. Not sure there's enough hole space to allow this.
My question, though, is that this is an original installation from about 25 years ago, it must have passed its initial installation certification. The last EICR I had done was in 2017, and it did not fail on this, not even a comment.
When did this requirement first appear, could it be that this was legal at the time but not now (if so this is a C3, not to current spec). Could the electrician feed one neutral into the lower CU and daisy chain it across the 3 MCB/RCD? If so it would mean only one new additional neutral fed from meter box rather than 3.