1 hour ago1 hr Hi I am building a 2 storey house with habitable loft rooms.The staircase is open plan into a hallway with direct access to the front door.Building regs have stated the route (from the loft room ) to ground floor exit must be a protected route.Can anyone shed some light on exactly what this means will fire doors to the bedrooms on the first floor be sufficient? And fireProof plasterboard in and around the stair caseSee stock image for general gyst of what staircase design will be
1 hour ago1 hr You're not a two-storey house for Building Regs, you're a three-storey house.. If you were two-storeys you could do what you show here, but as you have habitable rooms in the loft you must protect the stair. My understanding is that normally that means enclosing with fireproof materials, doors etc. Or you can get a misting system that meets the relevant standard and, depending on your Building Control person, have a Fire Engineer sign it all off too. At the moment they're not giving a huge amount of flexibility on Part B, so be prepared to argue your case properly. We are doing this right now so I know how painful this is (and expensive!) Good luck finding a Fire Engineer...
Just now1 min Your route down from the loft rooms needs to be enclosed with walls that have a minimum of 30min fire resistance. Doors at all levels opening onto that route need to be a minimum of FD20 (but FD30 are the most common so use those). Basically you are closing off the rooms that pose a fire risk from the only escape route for those occupants of the second floor.Be prepared to have BC query a stair ending in a large open hallway with plenty of furniture as per your picture. They may claim that is another room and the escape route could be compromised by not being extended to a final exit. I assume whoever that is handling your building regulation submission would be dealing with this.....
Create an account or sign in to comment