2 hours ago2 hr Author @Nickfromwales the air test option is very tempting, not sure if I'm brave enough. Obv we'll have to fill it eventually anyway so, maybe better just to get on with fitting the manifold and putting the water/glycol mix in 🤔
20 minutes ago20 min You can always do DIY manifold of just plumbing all the pipes together with push fit fittings, turn it into one massive loop.... Then pump the whole lot with a glycol mix!!
18 minutes ago18 min 1 hour ago, lizzieuk1 said:@Nickfromwales the air test option is very tempting, not sure if I'm brave enough.Obv we'll have to fill it eventually anyway so, maybe better just to get on with fitting the manifold and putting the water/glycol mix in 🤔Just check with your intended ASHP manufacturer to see if they don’t want / allow glycol etc, as it’s an absolute bastard to eradicate if so.
2 minutes ago2 min 11 minutes ago, Andeh said:You can always do DIY manifold of just plumbing all the pipes together with push fit fittings, turn it into one massive loop.... Then pump the whole lot with a glycol mix!!No need to pump. On my current MBC PH TF project the client and I mixed up two of the biggest gorilla flexi tubs with dilute glycol mix. I installed 15mm brass tank connectors at the bottom of each one with 1/4 turn valves for on/off, which we then ran an off cut of UFH pipe from and connected to the manifold. We raised these up on a few pallets at the high side of the plot, and let gravity do its thing, and from mixing the brine up to all the loops filled and purged (200m2) it was prob not much more than an hour.Just remember to stir the mix thoroughly, as neat glycol can congeal in the pipes, just use a £10 paint stirrer in a cordless drill.