Back-to-brick semi retrofit: MVHR blocked by a steel beam? Sanity check on a System 3 (continuous extract) plan

Featured Replies

We’re mid-way through a back-to-brick retrofit of a 1930s-style semi in York and need to settle ventilation in the next week or two. The electrician is at first fix and the window order is being finalised. I’d appreciate a technical sanity check.

The house

  • Semi-detached, three floors: ground, first, and a new rear dormer loft conversion. Plus a rear extension.

  • Roughly 175–195 m² treated floor area (architect’s figure 194 m²; my own measurement nearer 175).

  • Four bedrooms plus a first-floor office, which I’m treating as a fifth bedroom for ventilation.

  • Fabric: existing cavity walls filled and internally insulated to about 0.22; extension and dormer to current Part L; insulated slab; all new windows at 1.4. The pitched roof is insulated at rafter level, so the eaves are inside the warm envelope; the dormer’s flat roof is a cold, ventilated roof.

  • Airtightness: aiming high (taped membranes and sealed penetrations), but untested so far.

  • Heating: air source heat pump with a design load of about 4.5–5 kW; UFH on the ground floor and radiators upstairs. No open-flued appliances. The kitchen has a gas hob; the utility has an induction hob.

  • Wet rooms: kitchen/dining, utility, ground-floor WC (no shower), family bathroom, two en-suites.

The MVHR question
MVHR was ruled out earlier because a structural steel beam in the ground-floor ceiling prevents ducting across it. But most of the first-floor boards are now up, and there’s eaves space inside the envelope for a unit. Is radial MVHR realistic here, feeding the ground-floor rooms down through the first-floor void either side of the steel? Or does a beam like this normally kill it? I’d take MVHR if it’s viable. It’s worth roughly 850 W off the design heat loss, and everyone who has it seems to rate the comfort.

The fallback: continuous mechanical extract (System 3)

  • Upstairs: a central MEV unit in the second-floor eaves, extracting from the three bathrooms, discharging through the roof or the dormer cheek.

  • Ground floor: three through-wall dMEV units, in the kitchen/dining room, the utility and the WC.

  • Cooking: ducted cooker hoods in the kitchen and utility, in addition to the continuous extract.

  • Background ventilators: through-wall rather than trickle vents in the window frames, one per habitable room (two in the open-plan kitchen/dining room), none in the wet rooms. Acoustic models in the bedrooms if possible.

  • Boost rates: 13 L/s for the kitchen and utility, 8 L/s for each bathroom, 6 L/s for the WC, 56 L/s in total.

Questions

  1. Whole-dwelling rate under ADF 2021 Volume 1. By bedroom count I get 43 L/s for five bedrooms. Is there also a floor-area minimum (I’ve seen 0.3 L/s per m² mentioned) that would govern at this size? If so, the continuous rates across the extract points need to add up to around 52–58 L/s, which is more than my boost total. How do people normally split that between a central MEV unit and dMEV units?

  2. Background ventilator area. I’d assumed 4,000 mm² per habitable room. What’s the correct equivalent area for a continuous-extract system under ADF 2021?

  3. Products. Any recommendations for a quiet central MEV unit (one en-suite opens straight off a bedroom) and decent dMEV units? Sound levels at the continuous setting matter more to me than boost capacity.

  4. Detailing. What’s the best way to sleeve and seal through-wall vents and duct penetrations through internal wall insulation, using PIR with a vapour control layer, without compromising airtightness or creating a condensation risk?

  5. Ducting and controls. What duct type and size would you use for the central MEV runs in the eaves? Is a humidity-sensing boost plus a light-switch overrun the right control set, or is there something better?

  6. Gas hob. Any issues with a gas hob in a reasonably airtight house on continuous extract? Should the hood be ducted or recirculating?

Plans are attached (floor plans, elevations, and the ground-floor structural layout showing the steel). Thanks in advance. This forum has been invaluable in getting this far.

26-37-20-001 S1 Proposed Floor Plans.pdfE1030 - 01 - Foundation GA.pdf

You can sometimes make decent size holes in the web of a beam. Find out the MVHR duct requirements and ask your SE to accommodate?

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.