November 2, 20233 yr Can anyone help with a photo of their FTC6 DIP switch settings please? I cannot get mine to work with the outdoor unit, unless i have Sw4-1 and 2 on. Which seems like its making it think there is an outdoor unit, even though it isnt communicating. Once those 2 switches are set, FTC6 appears happy, switches the pump and valve, but the heat pump never actually starts! A frustrating unit. It is possible ive missed somthing or even that the outdoor unit is faulty... But im hoping its a setting.
November 3, 20233 yr I cannot get a clear enough photo but I can see on mine the following are ON: SW1 - 2, 3, 7, 8 SW2 - 8 SW3 - 5 SW5 - 2
November 3, 20233 yr Author Thanks so much. Figured out the problem is I've switched off SW2-8 as i dont have a flow sensor. This means that the unit is looking for a non R32 HP and so it failed on no comms! Mitsubishi were pretty helpful with this