pacemaker1000 Posted October 7, 2022 Posted October 7, 2022 I have two manifolds on two floors. Second floor is working perfectly, room stat calls for heat, actuators open, pump comes on and demand light comes on and calls for heat from the boiler. ground floor has suddenly stoped demanding heat? stats on, actuators open and pump comes on but demand light doesn’t come on and boiler won’t start? thanks
pacemaker1000 Posted October 7, 2022 Author Posted October 7, 2022 Had two red herrings.🙄 bulb gone in 'heat demand' tested with metre and ok. temperature sensor in wrong place. Was on 2nd manifold tee meaning only way it got heat was conductive and not flow. adjusted and boiler now comes on at 40 and off at 45
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now