I’m doing this retrospectively as house was built in 2021. I’ve been trying to get hold of the data but it’s like pulling teeth.
I believe this is the heat calc that was used by the heat pump supplier/installer
If you have a heat loss/load calc that says 10.3 kW, what output heat pump would be recommended (new build house, EPC B)
The MCS MIH documents don’t state clearly how many kW you need to allow for DHW and defrosting.
Appreciate you do not want to oversize it; but equally is there a danger of under specifying it?
If the rad is producing 285 watts and the calculated total heat loss for the bathroom is 643 watts, does that mean the rad has been incorrectly spec’d? Or someone has not accounted for the corrected output.
Why would the inlet temperature be higher than the output temperature?
That would give a negative answer to the Q (power) = Flow x SHC x (Flow-Rtn Temp)
House has UFH on ground floor. Rads in bathroom, bedrooms and en-suites on upper floors. Flow temp into bathroom rad is about 37-40C.
Screenshots of temp gauge on dining room (bifold doors) UFH manifold and the outlet/inlet temps on heat pump controller from yesterday.
Used 93kW in last 24 hours. Vast majority of that will have been heat pump; apart from lights, TV for a few hours, oven 1 hour, small electronic devices recharge.
Outside air temperature between 0 and +4C.
Would it be possible for someone with knowledge of this to confirm these figures, please, in relation to an aluminium vertical radiator in a bathroom:
Water temperature going into rad [flow in] is 40C and water exiting [flow out] is 35C.
Average temp in rad is 37.5C.
Target temperature of bathroom is 22C.
DeltaT is 37.5-22= 15.5C
DeltaT correction factor is 0.179 [from manufacturer]
Radiator Output at DeltaT 60C is 1661 Watts [from manufacturer]
Corrected rad output is 1661 x 0.179= 297.32Watts
Many thanks.