Hello everyone,
Last March, we had a Daikin Altherma LT R32 8kW system fitted last year, with a 160 litre DHW tank, running CHW for a 3 bedroom recently built house with good insulation. Radiators are all properly specified, flow temps set at about 42C in current 5C outside temps. The house gets warm with no problems, with 18C set-back temperature, and occasional rooms up to 21C (e.g. bathrooms in the morning, lounge in the evening). It's configured to use weather compensation, so dropping to 30-35C flow temperature as the outside temps warm up. Hopefully this is pretty much an optimal system.
The only thing is, I get poor SCOP - see below:
Looking at the CHW, this seems really low, and has since dropped to around 1.5! Back in April, we started hearing fizzing sounds, and basically the heat exchanger had sprung a leak and coolant gas was fizzing into the water loop. As there was less and less coolant going round, the system had to work harder and so the SCOP dropped. The heat exchanger was replaced at the end of April and the SCOP went back up from 2.58 to 2.93, and on DHW 1.78 to 2.34.
Well, back in October, it started fizzing again and the SCOP's on the way down too.
So... any ideas firstly what's causing the poor SCOP? This system is supposed to be about 3.5 to 5.5 SCOP, so 2.5-2.9 is pretty rubbish.
Secondly, any idea why the heater exchanger has failed again (so that's two brand new heat exchangers now that have gone)? I'm thinking the only reason they could fail is over-pressure or over-temperature. I do notice the hot gas inlet from the external unit is really hot, probably 55-60C - is that normal?
Any advice or experience with these Daikin units would be really appreciated. The original dimensioning seemed very sensible, with about a 5kW heat input required in really cold temperatures, so 8kW seems well-dimensioned. As I say, the house is warm, it's just really inefficient (and breaks heat exchangers!).
Thanks
Richard