Hi
I spotted this post while searching for Vaillant schematics for the Arotherm Plus.
(I was actually looking to see if new schematics had been released!)
I have that heat pump with a basic radiator setup, cylinder and 40l buffer tank/volumizer.
I had problems after installation with wildly varying and very high flow temperatures, heat curves not working and very poor performance.
I had undershoots and overshoots of room temperatures, all very confusing.
I am using basic system 10
It turned out that there is an issue in the controller logic (and the schematic) when using the VF1 sensor with a simple buffer/volumizer tank.
Following investigation by Vaillant It needs to be disconnected!!
The system then measures the flow temperature using the sensor in the heat pump.
The system then performs correctly using the heat curves and correct flow temperatures. (I use heat curve of about 1.0-1.1)
Performance is then hugely improved.
I have an overall CoP of 3.47 since the fix was applied (includes DHW) and got 3.67 Dec, 3.17 Jan and 3.54 so far in Feb.
Best heating Cop is 5.15 on 30th Dec, best DHW is 3.54
Overall very pleased with performance.
I have an accurate, certified MMSP monitoring system to measure inputs and outputs giving a CoP,
The Vaillant app and interface units seem to report an underperformance for me of about 18%, maybe rounding etc?
I strongly suggest that you contact Vaillant technical support, they have been great once the symptoms were identified.
The App does not show VF! temperature after the fix but it does show flow temperature as Heating Circuit 1 for me.
Hope it may help