Best bet is to have all the pipes/ducts run under the sub-base and then come up vertically through the insulation and slab.  It needs very careful laying out to get all the services in exactly the right location, plus ducts need to be run with gentle bends, so things like MDPE water pipe can be pulled in OK (or in our case a fat three core power cable).

Link to comment
Share on other sites

2 minutes ago, JSHarris said:

Best bet is to have all the pipes/ducts run under the sub-base and then come up vertically through the insulation and slab.  It needs very careful laying out to get all the services in exactly the right location, plus ducts need to be run with gentle bends, so things like MDPE water pipe can be pulled in OK (or in our case a fat three core power cable).

And through to every room they're needed? Would you expect your slab contractor to specify what's required or do you need to specify it for them?

Link to comment
Share on other sites

In our build soils/wastes went under the slab.  UFH pipes in the slab.  A couple of ducts for kitchen island and floor sockets and everything coming in through ducts under the slab and up into the plant room. All (including water) were then run around the house in service voids in walls/ceiling  starting from from the incoming points in the plant room.

 

Our ducts for the kitchen and recesses for floor sockets were too small...had to be hacked about.  Every single one of our soil pipes/wastes was in the wrong place. Plans  wrong, no one noticed architect had drawn the things wrong not corresponding to bathroom layouts so my wall hung w.c.’s would have been a good 8 inches out from the wall,  Slab had to be hacked out to realign it was very worrying due to UFH

 

We are single story so every bathroom was wrong.

 

The whole slab thing was utter hell.

Edited by lizzie
Link to comment
Share on other sites

39 minutes ago, eandg said:

And through to every room they're needed? Would you expect your slab contractor to specify what's required or do you need to specify it for them?

 

Usually water, telephone, electricity just needs to enter in one and then the internal pipes, cables take over.

 

Drainage positions needs to be considered before the slab is poured.

 

On our build (we didn't have a single contractor) the internal drainage did seems to be a job of with it being a bit unclear as to who is responsible, luckily our brickie and plumber were pals so was not an issue.

 

If you have a slab contractor I would think it was their responsible, but  I would clarify.

Link to comment
Share on other sites

As a note of caution, you are not allowed to run power cables in the same duct as telecommunication cables.  Best to have a duct for each service that comes up through the slab.  As @lizzie has pointed out, it is your responsibility to get all these services coming up through the slab in the right places; as I mentioned above, accuracy in getting these spot on is critical and it's one of those key interface areas where you need to be certain that the people running the ducts and pipes in (often the ground works team) have got them all in exactly the right location.

Link to comment
Share on other sites

50 minutes ago, JSHarris said:

As a note of caution, you are not allowed to run power cables in the same duct as telecommunication cables.  Best to have a duct for each service that comes up through the slab.  As @lizzie has pointed out, it is your responsibility to get all these services coming up through the slab in the right places; as I mentioned above, accuracy in getting these spot on is critical and it's one of those key interface areas where you need to be certain that the people running the ducts and pipes in (often the ground works team) have got them all in exactly the right location.

 

Did you get any of these into contracts, or was it case of meticulous supervision by you, @JSHarris? This is presumably to something like +-5mm, perhaps 10mm.

 

A downside of achieving that would be to make change difficult wrt the plans linked to the contract, whilst not doing that means the risk falls on the self builder.

 

I think that I would look into dealing with this by putting the big ones into the slab eg soil pipe, whilst using some arrangement in the floor buildup for electricity distribution, combined with as little service void as possible. I do not have a mature scheme of this type for a new build, however.

 

Ferdinand

 

 

Edited by Ferdinand
Link to comment
Share on other sites

All down to supervision and cross-checking by me, I'm afraid.  I did put the exact location of everything coming up through the slab on the drawings that were part of the ground works contract, with allowable position tolerances, but the contractor thought I was crazy in stipulating such precise positions.  On his last day on site I insisted we get the total station out and accurately check the position of everything.  He grudgingly obliged, and I was happy things were OK, but the soil pipe ended up being mighty close to the inside face of the North wall, and caused me about a days work to chip around the slab and get enough clearance to move it maybe 20mm.  My fault, the tolerance on the position I put on the drawings (+/- 40mm) was too great, it should have been about +/- 20mm.  All positions were referenced to a fixed post, with a marker, at the corner of the plot.

Link to comment
Share on other sites

One of the reasons I am contemplating a "wet wall" --type of construction ==so there is a walk in service access( for slim folk ) down north side of house  where you want few windows .

from one end connected to service room 

a waste of space you may say --but any alterations in future can be done without destroying and internal finishes.

may not be possible --we will see 

Edited by scottishjohn
Link to comment
Share on other sites

If you think you might be planning a future garage, summer house, home office, (hot tub?) etc then worth thinking about cable ducts to go out under the slab if your cu is in a plant room within the house. Ditto ducting if your planning hardwired CAT, CCTV etc to a remote building.

 

Similarly if you're planning an ASHP then ducts in for the pipework and power, insulated ducts in the case of the ASHP possibly or big enough to take pre insulated pipes.

Link to comment
Share on other sites

You need to talk to an engineer. We are having a passive slab & he wanted non made up ground, I am sure there are ways round it (presumably at a cost!), but you need to go with what they say. It would be worth contacting Hilliard Tanner in Ireland if your engineer isn't that familiar with this method of construction. 

Link to comment
Share on other sites

Thanks both. We are/were waiting to get a design sorted before contacting a structural engineer but will get onto it asap. 

 

The ducting/cabling is one I'll need to get my head round - are there any straightforward guides about? I watched a few videos of passive slabs last night and they looked to be completely without anything bar EPS and concrete!

Link to comment
Share on other sites

2 minutes ago, eandg said:

Thanks both. We are/were waiting to get a design sorted before contacting a structural engineer but will get onto it asap. 

 

The ducting/cabling is one I'll need to get my head round - are there any straightforward guides about? I watched a few videos of passive slabs last night and they looked to be completely without anything bar EPS and concrete!

 

Our passive slab was laid on a  bed of whacked down coarse stone:

5741978318605_Housebase-Copy.thumb.JPG.182ed4223419def89122bf1c53810cdb.JPG

 

You can just see the pipes and ducts coming up through this, they were all placed accurately in trenches underneath the sub-base.

 

Next the sub-base stone was blinded and levelled with grit, to form a dead level bed for the shaped EPS blocks and sheet:

 

5742a9d725edb_Housebasegoingdown2.thumb.JPG.2cb63fd645aa16f7221ee11a83c6b10b.JPG

 

You can see some pipe/cable ducts poking up at the back of this photo.

 

Once the foam blocks and sheet were all laid, a DPM was laid and sandwiched between the top foam sheet and the two underneath, the reinforcing steel was added and tied in and the UFH pipes were laid and tied to the steels:

 

 

5742a9e1b7acd_Housebasegoingdown3.thumb.JPG.a63fda24b89aa8a83265410681437f1e.JPG

 

The day after the photo above was taken the concrete was poured and trammelled roughly level, as shown in this photo:

 

5742a9e52e8b2_Housebasegoingdown4.thumb.JPG.c34a2fdab7c02c6aa53c109c606ba0f8.JPG

 

A couple of hours after the photo above was taken the slab was power floated smooth, leaving a finished floor that was flat and smooth enough to tile and floor to directly, with no need for screed or levelling compound.

 

 

Link to comment
Share on other sites

  • 1 year later...
On 11/03/2019 at 16:56, Jeremy Harris said:

 

Our passive slab was laid on a  bed of whacked down coarse stone:

 

.....

 

On 11/03/2019 at 06:59, Nick1c said:

You need to talk to an engineer. We are having a passive slab & he wanted non made up ground, I am sure there are ways round it (presumably at a cost!), but you need to go with what they say. It would be worth contacting Hilliard Tanner in Ireland if your engineer isn't that familiar with this method of construction. 

 

Thanks @Jeremy Harris for sharing details of your passive slab. One further detail I would like to know is how the trenches were done and made up. Unfortunately the building regs don't have clear guidance on how to lay drains under a passive slab, and I've got an engineer suggesting that the drain should be encased in concrete! (which I'm hoping isn't necessary). It was my impression that the drains and services should only need to be in a bed of gravel, in a trench dug after having compacted the sub-base (but perhaps what they do in other countries isn't appropriate here).

 

Unfortunately @Nick1c I don't think my engineer is very familiar with the system (Jackon Atlas in my case), but I don't really want to be contacting an engineer in Ireland.

Link to comment
Share on other sites

32 minutes ago, Ross said:

Thanks @Jeremy Harris for sharing details of your passive slab. One further detail I would like to know is how the trenches were done and made up. Unfortunately the building regs don't have clear guidance on how to lay drains under a passive slab, and I've got an engineer suggesting that the drain should be encased in concrete! (which I'm hoping isn't necessary). It was my impression that the drains and services should only need to be in a bed of gravel, in a trench dug after having compacted the sub-base (but perhaps what they do in other countries isn't appropriate here).

 

This is what out building inspector asked for:

  1. All drains are 110mm UPVC and have straight runs with minimal connection points below the slab.
  2. All drains are to be bedded and backfilled with 10mm pea shingle and the slab is reinforced.
  3. Drains serving as SVP’s to first floor are to have 200mm long rest bends at base with concrete support.

Could it be there is a mix-up regarding the concrete supports?  What passive slab system are you using?

 

Quote

It was my impression that the drains and services should only need to be in a bed of gravel, in a trench dug after having compacted the sub-base (but perhaps what they do in other countries isn't appropriate here).

 

This is exactly what we did.  See this post, you can just about see the concrete support in the drainage picture.: 

 

 

Edited by Dan F
  • Like 1
Link to comment
Share on other sites

7 hours ago, Dan F said:

 

This is what out building inspector asked for:

  1. All drains are 110mm UPVC and have straight runs with minimal connection points below the slab.
  2. All drains are to be bedded and backfilled with 10mm pea shingle and the slab is reinforced.
  3. Drains serving as SVP’s to first floor are to have 200mm long rest bends at base with concrete support.

Could it be there is a mix-up regarding the concrete supports?  What passive slab system are you using?

 

 

This is exactly what we did.  See this post, you can just about see the concrete support in the drainage picture.: 

 

 

+1 to above. We did exactly the same on our build

  • Like 1
Link to comment
Share on other sites

8 hours ago, Ross said:

[...]

but I don't really want to be contacting an engineer in Ireland.

 

I have worked with Hilliard Tanner in Ireland for four years: slab, Durisol, steels, louvres. He has been on site exactly the same number of times as the other SEs with whom we have worked.

 

0 , Zero.

  • Like 1
Link to comment
Share on other sites

Thanks for the helpful replies. Good to know what other people are doing.

Another ignorant question: Can a water supply pipe go in the same trench under the slab as the soil drain pipe?

Link to comment
Share on other sites

1 minute ago, Ross said:

Thanks for the helpful replies. Good to know what other people are doing.

Another ignorant question: Can a water supply pipe go in the same trench under the slab as the soil drain pipe?

 

Not sure who is doing your slab or what they do, but a typical approach is to use a 110mm UPVC pipe with a shallow bend for water supply and then to put MDPE through this afterwards.   A 200mm shallow bend will just about work with 32mm MDPE assuming you feed it through from inside.  (we were worried about this).

  • Like 1
Link to comment
Share on other sites

Regarding the MDPE water pipe and its inflexibility, and relying on a swept-bend to get it in, why not simply place a 90º MDPE elbow at the bottom where the pipe turns vertical?

 

I have been told such joints are fine to be inaccessible. Is that wrong advice?

  • Sad 1
Link to comment
Share on other sites

2 minutes ago, Dreadnaught said:

Regarding the MDPE water pipe and its inflexibility, and relying on a swept-bend to get it in, why not simply place a 90º MDPE elbow at the bottom where the pipe turns vertical?

 

We were advised to avoid any/all joints in MDPE if at all possible. Also for any joints, if required, to be accessible.  That doesn't mean an elbow won't work, it will, I just think that most people would typically try to avoid it.  In our case, it needed a bit of help, but 32mm went round 200mm bend OK.

  • Thanks 1
Link to comment
Share on other sites

3 hours ago, Dreadnaught said:

Regarding the MDPE water pipe and its inflexibility, and relying on a swept-bend to get it in, why not simply place a 90º MDPE elbow at the bottom where the pipe turns vertical?

 

I have been told such joints are fine to be inaccessible. Is that wrong advice?

Nope, don’t do it. Although they are bullet proof fittings, how will you get to it if it has a problem. 

Full length of pipe from out side to inside, in a duct just in case of problems. 

 

To prove this i have already changed my new pipe by just pulling a complete new one in through the duct. 

I wanted a bit more pipe to come up into the plant room so just pulled out the old and slid in a new pipe. 

You will not do that if you have joins or elbows. 

Edited by Russell griffiths
  • Like 2
  • Thanks 1