Party walls noise insulation


Terryturf1

Recommended Posts

Ok so i asked the building control officer what insulation to put between my party walls 

Im dividing an 18m×12m portal frame barn into 3 houses 

He advised me to employ an acoustic company to advise

Surely theres some format to this . I am using cavity wall blockwork 

So what can i do other than use the acoustic slab wool insulation then maybe some special noise proofing plaster on these walls after

Help!!@

Link to comment
Share on other sites

If you are using cavity walls then use the heaviest block possible and also make sure every joint including the perp ends are fully mortared. Sound gets through the tiniest gap, and you need to make sure that you get mass in the walls. 


What cavity can you afford to leave ..?

Link to comment
Share on other sites

If the third party company will give you a guarantee on the result, then I would attach a high value to that, as getting it wrong can have a big downside.

 

Sound insulation is pretty basic, and expensive to improve afterwards I think as it is buried deeply. So if you DIY it, then have a plan B for improvement for when the test engineer sucks his teeth and goes "sorry, Guv".

 

Plan B might be, if permissible, to not cosmetically fit out the next one until you have sound tested the last one, so you can beef it up on the other side in Unit 2 without having to half-demolish the interior of Unit 1 to get it back to a point where you can do the work.

 

I think you could *maybe* get some decent advice from Building Control on this, because they always want houses that work.

 

Ferdinand 

 

Edited by Ferdinand
  • Like 1
Link to comment
Share on other sites

Assuming under English Regs Appr Doc E has masonry cavity wall and solid wall options that ‘should’ work but need testing on completion. Alternative is to look at Robust Details (RD) and follow their design details. Unfortunately this only covers new build, not conversion, so testing probably still required unless you can convince BCO otherwise.  As above detailing to avoid flanking transmission is critical as is quality of workmanship. Adding mineral wool in the cavity gives little, if any,  acoustic benefit as the acoustic performance is down to the mass of the wall and 2 decoupled leaves.

Mineral wool rolls or slabs, at least 18 kg/m3, are needed to prevent party cavity wall thermal bypass - a thermal requirement reducing the party wall u-value to zero (See Appr Doc L1). This may not be so critical with conversion work but check with your BCO. The RD view is that this measure must not degrade the acoustic performance of the wall hence they show both filled (optional) and unfilled  cavities.

Link to comment
Share on other sites

9 hours ago, Terryturf1 said:

De coupled leaves ? Are you saying not to use brick ties ?

 

no he is not, use resilient ties wall ties (Type A) correctly spaced (i.e. not too many of them).

 

What @Mr Punter is describing is too much mortar build up / snots on the ties will cause bridging of the cavity and reduce the acoustic performance of the wall. 

 

This is particularly of note if using insulation slabs / roll in the cavity as careless brickies can let build up happen on top of the insulation slabs / roll which causes issue.

 

Edit: if you find things like below, you want to be having a lot of words with your brickies!

 20191016_092617.thumb.jpg.6aa7d6cf69e5b26e16628d919384348b.jpg

Edited by Moonshine
Link to comment
Share on other sites

18 minutes ago, ADLIan said:

mortar droppings on ties and bottom of cavity!

 

Mortar at the base of the cavity is not usually a problem on open cavities unless the is a gas/pollution membrane at the foot of the cavity (at floor level). If there isn't this in place then mortar will just drop down to the oversite level and not a big issue acoustically. The big issue acoustically comes where there is a gas/pollution membrane at the foot of the cavity and the mortar gets trapped and the brickies don't clear it out.

 

A way around this is to keep blocks out at the base of the cavity to allow cleaning of mortar droppings.

 

1250744224_20190913_133221(Large).thumb.jpg.73fb7619dc62c9c4ec444b2f5c3d7dfb.jpg

Edited by Moonshine
  • Like 1
Link to comment
Share on other sites

I'm going through exactly this at the moment. Architect and BC both said to get advice from the company that will be doing the test. 

 

I've contacted half a dozen companies, some want to see drawings before quoting. 3 companies gave ballpark costs - all roughly same for the actual testing (just shy of £400+vat). 

Massive variety of advice cost though - from £80 to £700 depending on how much they hold your hand. 

Edited by Jenni